Turns up to a house today, owner calls me in after having the down ring MCB constantly tripping after 30 secs.
I go in and check it out to find a nice new £50 BG CU (B&Q jobbie) recently installed.
I take the cover off the CU to find that all the connections are loose and needed approx 2 turns to get them right.
1 earth cable is not connected and is just left floating in the CU
I also find that quite a few of of the N and E conductors were biting onto the outer insulation
Loads of the threads were stripped so some screws were not biting.
Worse of all, the installer has taken out an RCD and the live RCD strapping cable are floating LIVE in the CU.
The owner was very coy and I did not get the full story, it seems that originally the RCD was tripping before the MCB so someone took out the RCD, then the MCB started tripping so the owner had to call a proper sparks.
The fault turned out to be a moisture in a back box on an outside socket.
This CU would have def been a fire a few years down the line!
I think and got the picture this was done by one of his mates "who knows a bit bout lectrics mate" and "I'll do it cheap for ya mate".
I go in and check it out to find a nice new £50 BG CU (B&Q jobbie) recently installed.
I take the cover off the CU to find that all the connections are loose and needed approx 2 turns to get them right.
1 earth cable is not connected and is just left floating in the CU
I also find that quite a few of of the N and E conductors were biting onto the outer insulation
Loads of the threads were stripped so some screws were not biting.
Worse of all, the installer has taken out an RCD and the live RCD strapping cable are floating LIVE in the CU.
The owner was very coy and I did not get the full story, it seems that originally the RCD was tripping before the MCB so someone took out the RCD, then the MCB started tripping so the owner had to call a proper sparks.
The fault turned out to be a moisture in a back box on an outside socket.
This CU would have def been a fire a few years down the line!
I think and got the picture this was done by one of his mates "who knows a bit bout lectrics mate" and "I'll do it cheap for ya mate".