Morning!
Been handed the job of 'running' a sub main to an out building using the spare phase of a split phase system.
Now, the set up..
There is a 25mm 2 core SWA starting from the supply end for about 15M to a tractor store with a metal enclosure where the cable has been cut to terminate in to a metal enclosure to then T off to supply a small DB for a couple of sockets and lights, meaning ill be using the armouring as the CPC, which again roughly works out to be around 50mm2.
The 2 core then proceeds to a large storage unit for again, a couple of sockets and lights.
Now, from my basic calcs this allows for a 40A capacity as the run is just under 50M in total.
Question is, earthing.
There is already a 16mm running from an earth rod to one unit using the first phase, so can i just pull that out and terminate it onto a earth block and split that between the phases/buildings?
Or, could i install an separate earth rod away from the intake position (15M) at the first cut point (dirt externally) and in effect 'backfeed' the CPC for the first run back to the intake and on to the other out building basically making a T with the earthing each way via SWA.
Been handed the job of 'running' a sub main to an out building using the spare phase of a split phase system.
Now, the set up..
There is a 25mm 2 core SWA starting from the supply end for about 15M to a tractor store with a metal enclosure where the cable has been cut to terminate in to a metal enclosure to then T off to supply a small DB for a couple of sockets and lights, meaning ill be using the armouring as the CPC, which again roughly works out to be around 50mm2.
The 2 core then proceeds to a large storage unit for again, a couple of sockets and lights.
Now, from my basic calcs this allows for a 40A capacity as the run is just under 50M in total.
Question is, earthing.
There is already a 16mm running from an earth rod to one unit using the first phase, so can i just pull that out and terminate it onto a earth block and split that between the phases/buildings?
Or, could i install an separate earth rod away from the intake position (15M) at the first cut point (dirt externally) and in effect 'backfeed' the CPC for the first run back to the intake and on to the other out building basically making a T with the earthing each way via SWA.