Carried out a Ze (E3 Method) reading of the Earth Electrode today. Assuming the ground is mostly if not completely consisting of chalk. Reading was 300 Ohms. Of the top of my head i recalled 200+ may be unstable. However after consulting BS7671 I cant quite decide what action needs to be taken.
Its TT Earthing arrangement, distribution circuits so maximum Zs of 500 Ohms. I initially thought install another Electrode to try and reduce the resistance. However after reading 411.5.3 which referred me to 542.2.4 - "The type and embedded depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value".
I will most likely install another electrode but is it necessary? How would you confirm 542.2.4? I was thinking maybe coming back during the peak summer when its going to be the driest and carrying out the test again? Am I missing anything?
Its TT Earthing arrangement, distribution circuits so maximum Zs of 500 Ohms. I initially thought install another Electrode to try and reduce the resistance. However after reading 411.5.3 which referred me to 542.2.4 - "The type and embedded depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value".