TT reading above 200 Ohms...

Carried out a Ze (E3 Method) reading of the Earth Electrode today. Assuming the ground is mostly if not completely consisting of chalk. Reading was 300 Ohms. Of the top of my head i recalled 200+ may be unstable. However after consulting BS7671 I cant quite decide what action needs to be taken.

Its TT Earthing arrangement, distribution circuits so maximum Zs of 500 Ohms. I initially thought install another Electrode to try and reduce the resistance. However after reading 411.5.3 which referred me to 542.2.4 - "The type and embedded depth of an earth electrode shall be such that soil drying and freezing will not increase its resistance above the required value".

I will most likely install another electrode but is it necessary? How would you confirm 542.2.4? I was thinking maybe coming back during the peak summer when its going to be the driest and carrying out the test again? Am I missing anything?
 
300 ohms Ze on TT is fine under the 500 max Zs, chalk dries fast though so it could easily go over in summer and breach 542.2.4. I'd bang in a second rod in parallel and re-test.
 
If you use the extendable rods using 2 or even 3 (ie going 2-3 m deep) the surface area to the soil is greatly increased thus bringing down the resistance.
I've never found putting another 'like for like' in parallel has proved to be significantly better.
 