TT Sub Main Fault Protection

Hello all,

Could I have some advise on this scenario please;

TT System

Upfront Overcurrent + Variable Earth Leakage Relay

Currently Set At 500mA + 1000ms delay for selectivity between other devices

Supplies a B63A MCB which goes to a reception DB.

Max Measured Zs End Of Line = 70 Ohms

My issue is our test equipment doesn’t allow for anything over >750ms.

I turned the delay to 0.5s and retested and this was 605ms before setting back to 1.0s.

Obviously this needs to achieve the 1.0s disconnection time so what would be the acceptable limits?

I’ve only had a quick look but when accounting for total measured disconnection time it includes;

Intentional Delay
Relays internal Operating Time
Shunt Trip Operating Time

Thanks all.
 
You only need to show it disconnects within 1s. If your equipment
This forum is an ad nightmare now. Not even sure how to edit my post because so cluttered in ads.

If you can set RCD a bit higher but within the limit of your meter so you can confirm disconnection at 500mA at near 750ms (so you can record a value), then just record that. That is fine as is within the 1s. What is the next RCD down stream you are trying to achieve selectivity with?
 