I am going to change a guys CU, the CU is in a 4 bed cottage out in the stix, its on a PME system, now I have done a periodic on the cottage and all good so the CU is a go ahead but while I was there I noticed a half used roll of 16mm T+E, after talking to the customer he explained that the 16mm was in plastic conduit buried, he had left an inspection pit and all looks good, its going into a KMF at the other end which is a seperate annex to the cottage and the customer is currently doing it up with a new bathroom, bedroom and lounge, and eventually want's it connected up to the mains with a new CU in the annex hence the 16mm T+E he has already installed.

He was asking me the best way to connect it up and he actually wants me to connect it up for him when the time comes, (he will want me to also put the new CU in and a couple of lights and sockets).

Anyways, the reason for the post.

When connected up I was going to put a spike in now I know there's a lot of myth's and issues with exporting/extending PME earthing.

Whats your guys thoughts?

Cheers
Ash
 
Only real issue is if there are any extraneous conductive parts in the annex, an earth will have to be run back to the MET in the house. Hic.

Edit: I'm drunk and don't know if that actually makes sense. Just re-read the OP and can't focus on it at all.
 
you can check for extranious using your IR setting on your MFT....
anything less than 22 K ohms....then you can treat that as extranious....
so in that case you pull in a 10mm G/Y together with your twin....
 
Hi All,

Just wondering your guy's thoughts on this...

I am going to change a guys CU, the CU is in a 4 bed cottage out in the stix, its on a PME system, now I have done a periodic on the cottage and all good so the CU is a go ahead but while I was there I noticed a half used roll of 16mm T+E, after talking to the customer he explained that the 16mm was in plastic conduit buried, he had left an inspection pit and all looks good, its going into a KMF at the other end which is a seperate annex to the cottage and the customer is currently doing it up with a new bathroom, bedroom and lounge, and eventually want's it connected up to the mains with a new CU in the annex hence the 16mm T+E he has already installed.

He was asking me the best way to connect it up and he actually wants me to connect it up for him when the time comes, (he will want me to also put the new CU in and a couple of lights and sockets).

Anyways, the reason for the post.

When connected up I was going to put a spike in now I know there's a lot of myth's and issues with exporting/extending PME earthing.

Whats your guys thoughts?

Cheers
Ash
i`m pleased you have consulted in here first...

dont you tell him owt....

its your job....you do the job correctly....you collect the cash..

dont you tell `im owt else on how to do this, that and`t other...
 
If there is any extraneous services pipework or the like, then the annex will need an additional 10 mm g/y bonding conductor when extending a PME earthing system. T&E in plastic buried conduit is not the right way to go about distributing sub-mains and the like underground. SWA is the cable of choice, when that cable is to be buried either directly, or in a duct etc...

If you have a perfectly good PME earthing system, don't be a chump and TT this annex!!
 
If there is any extraneous services pipework or the like, then the annex will need an additional 10 mm g/y bonding conductor when extending a PME earthing system. T&E in plastic buried conduit is not the right way to go about distributing sub-mains and the like underground. SWA is the cable of choice, when that cable is to be buried either directly, or in a duct etc...

If you have a perfectly good PME earthing system, don't be a chump and TT this annex!!
this is why i was pleased that he came asking in here first....

totally ridiculous..
 