cliffed
What's your thoughts on a 2.5mm earth conductor to earth electrode supplying dist board,bonding 10mm to gas & water,crazy or what,the earth system is a tt
earthing conductor should be mechanically protected if it's only 2.5mm. what's the Ze/Ra/ PEFC?
Ze 19 ohms pefc 10 amps 30ma rcd,just seems ridiculous that they managed to install 10 mm to main bonding but used 2.5mm to db's,it's mechanical protected to spike cheers
Well if it has mechanical protection it is fine 2.5mm earthing conductor.Also, If I install new bonding on a TT system I still install 10mm to future proof it if it gets changed to TN-CS.