got some bs3871 type 4 mcbs on a job 100a 63a 45a all come in over max allowable Zs
or am I working this out wrong ??
 
Zs values for type 4 of those ratings are extremely low. you'll probably find that the Ze alone is greater. only solution is a RCD.
 
got some bs3871 type 4 mcbs on a job 100a 63a 45a all come in over max allowable Zs
or am I working this out wrong ??

Someone on the original install didn't take into account the much lower Zs values that are required for the type 4 MCB's!! As Tel states the easiest solution is now, adding RCD('s)

Far too many electricians will even today, rely on the additional RCD protection when installing type D MCB's rather than designing the circuit(s) correctly. They are fast becoming, if not already become, the cover-all solution for all manner of non complying installation lash-ups!!
 
You need to get the manufacturers values for max Zs mate. I had this same problem on an EICR last year. I was surprised how much lower the max Zs from the manufacturers were, compared to the calculated ones.
 