Hello Marconi,

I've just seen your response as I was typing my note above. The new(ish) specs now state that only double pole RCDs and MCBs are to be used. In fact in my local building merchants they now only stock/sell double pole items.

Now I now what to look for a little digging on the internet appears to confirm you theory of a 2 phase supply. Sorry, my nomenclature is probably wrong but I understand what you are saying regarding both Lines being energised.

I'll post an update on Monday if anyone is interested.
 
It does not matter whether it is supposed to be regular single-phase with earthed neutral, two lines from 3-phase delta, 2-phase or whatnot... No circuit conductor of a 230V supply should be 345V from earth. If those readings are correct, either what you think is earth isn't, or there's something badly wrong at the supply end! Get it checked en seguida!

The fact that the voltages are all under 230 when you disconnect the rod, but the L-E is near the line voltage of a 3-phase system when it is connected, suggests the rather worrying scenario that the star point of the transformer has lost its earth, and one line (not the one feeding you) is leaking heavily to, or shorted to earth. This will be affecting all other consumers on your line and the other unfaulted line similarly, while the ones on the faulted line will be seeing what looks like a polarity reversal.
 
Last edited by a moderator:
Definitely sounds like neutral fault on supply side and if a 3 phase this often happens. 3 phase in street, not necessarily to the property.
 
LN wrote: ...suggests the rather worrying scenario that the star point of the transformer has lost its earth, and one line (not the one feeding you) is leaking heavily to, or shorted to earth.

I wonder if you think these small changes are allowable:

....suggests the rather worrying scenario that:

a. the star point of the transformer has lost or has a weak earth;
or
b. one line (not the one feeding you) is leaking heavily to, or shorted to earth;
or
c. in another installation fed by the transformer one line has been deliberately/erroneously connected to earth to create an earthed neutral.
 
We can reasonably assume that the neutral conductor is properly continuous to the star point as the L-N voltage is correct and the OP doesn't mention connected equipment malfunctioning as would happen if the L-N voltage varied widely. We can probably also assume that it is 3-phase at the substation, rather than split-phase, since on a split-phase system with a lost earth reference the L-E voltage would be the algebraic sum of the L-N and N-E. Since this is not the case here, it is likely that the source of the voltage between N (approx same as star point) and mass of earth is out of phase with that of the OP's line, hence probably unusually high leakage from another line. Therefore the highest voltage anywhere on the secondary must be 415V, of which 345V appear to be between the zero wire (that should be neutral) and mass of earth.

Unfortunately here our data runs out. We don't know the phase angle between the L-N and N-E voltages, so we can't use triangulation to calculate the relative magnitudes of the zero sequence leakage (which tends to hold the star point near earth due to symmetry) and the leakage that is causing the abnormal voltage. Therefore we can't calculate the relative impedances of the faulty N-E connection and the leakage. Academic anyway, as it's someone else's job to fix!
 
In my interpretation (#14) I have assumed a 3 wire 3 phase system without a neutral - 3 lines used for distribution, 240V between lines. Also poor ground conditions for the flow of earth currents hence my use of the term 'local star point' and the implied consequence of relatively high impedance between local and transformer earths.

I could well be wrong - but it came from a comment in an IET forum on how the 120V was upgraded to 240V in rural areas. ( see mdhamish at IET Forums - Wiring in Spain - http://www.----------/forums/forum/messageview.cfm?catid=205&threadid=6282)

I could not find much information on Spain's LV network other than Schneider saying Spain has 400V using 3 and 4 wire distribution.

Perhaps the OP can look out the window and tell us how many conductors he sees on any poles carrying the current to homes?

As you say - enough speculation. :-)
 
I have assumed a 3 wire 3 phase system without a neutral
The problem with that assumption is that, on a 3-phase delta system, there shouldn't be anything as high as 345V present anywhere, even with any combination of faults (barring freaky scenarios such as both a lost reference and someone having a large step-up autotransformer with a fault on the output pushing the whole distribution system off centre). The highest voltage that can be expected to appear with a combination of faults would be if the two lines other than the OP's line were leaking with equal impedance to E, and his line was not leaking at all. That would put the E midway along the vector between those two lines, creating an L-E voltage of *not what I just said, hang on..* f the readings are correct, I maintain that by far the most likely configuration is a 240/415V 3-phase 4-wire system.
 
As you point I have made a blunder. One would need a 4 wire star system 240/415V and not a 4 wire star 140/240V nor 3 wire delta 240V to obtain 345V L-E.

:)
 
And I too made the error of adding the phasors, expecting a voltage between 240 & 415, out of sheer force of habit, which I got. Of course the voltage in that situation would be sqrt((240)²-(240/2)²)=207V.
 
Apologies just for confirmation. All I saw was " the readings are correct".

Assuming my feed is 2 conductors from the 4 wires is that the case?

I'll go into my field tomorrow as the supply line passes through it and see if I an tell how many conductors there are.

I won't be cancelling the electrician either way as I want him to confirm everything is OK from my side before I call FENOSA.

I would like to have an understanding of what system I may have so I can prepare the Spanish words and understand what he tells me with regards to the supply.

Thank you
 
Potencia, retorno, tierra...
all you need to know. My experience of Spanish electricians is all good. OK, some existing (and some new) installations are just carp, but I have found that bringing an electrician in is just such good value and well worth it. They are well used to the old junk, and quite clued in to the newer ways...indeed, my CU has had to be updated twice in the last 10 years...I'm just waiting for Endesa to tell me I need a metal one! And don't forget, they do a good job at €17/hour...
I first-fix at 12...includes a pie and a beer at 9am on a 20 minute break for breakfast...in the sun! Perfect!
 