Can someone remind me, I can't find this in regs.
I recall from lessons that if one alter part of a circuit, then the entire circuit now needs to be upgraded to current regs?
Is this the case? - where is it found?

For example, say I take a existing ring final which has had a recent periodic (and OK). Just for example, say it might have some cables outside a zone, or clipped too close to the surface, or perhaps smaller detail like backplates without gromets or without earth sleeving.. Yet otherwise it's in good condition and measures well.
Let's say I need to extend this ring.
Does the entire circuit need to comply now? - ie would I need to replace the older parts with cables not complying back into zone, and to fix all detail like gromets/sleeving etc?

Justin
 
No, it's just the new work that has to comply. However, if you know that there are things that are not so great, whilst you've got the tools out, why not fix some of them?

However, you also need to remember that you might need to retro fix any serious issues like bonding, earthing or protection (rcd) in order for your new work to comply anyway.
 
Page 4 in the introduction

"This does not necessarily mean that they are unsafe for continued use or require upgrade" when talking about existing installations and alterations and additions.

There are no regs saying you need to grommets Reg 522.8.1 tells us about sheathed cable not being damaged during installation or maintenance, and grommets ensure this, but if there are none fitted and the sheath is not damaged then don't retrofit. .

Again in the regs Regulation 514.4.2 tells us that bare protective conductors and busbars should be sleeved G/Y and that is also endorsed in reg 514.4.6. Personally if I found bare conductors on a CPC, on a switch or socket I would sleeve FOC, if every connection never had the sleeve, then I would only sleeve if I were paid to do so, after all I don't run a charity.

Zones the same, If an existing installation had cables run out of zones then I would just advise the customer. If they paid me to redirect the cables I would.

As for extending a ring, then yes your work must comply with the current regs, so if you say fitting 2 extra sockets on an existing ring and bury the cable or the sockets needed protecting under reg 411.3.3, quite often you could fit a RCD FCU which covers your work.

For me to be honest that seems a little silly to just cover the 2 sockets with RCD protection, and have the remaining say 8 sockets not protected, and there could be one of these 8 that the customer uses to mobile equipment out door. I always liked to advise the client for perhaps just a few pounds extra instead of fitting a RCD FCU, I could fit a small enclosure at the main board with a stand alone RCD feeding the whole RFC.

Bottom line is though cost and what someone is willing to pay
 
You need to make sure your new addition is compliant with 17th Edition. However, the regs state that the circuit to which you are connecting too, must be able to satisfactorily maintain function and integrity with your new circuit added.
 
OK. That's all good then.
Common sense prevails for existing parts of a circuit even if I extend it.
If the old parts are still safe, then leave alone and advise. Fix the details if quick and affordable or paid for.
 