On a extension of a kitchen is a fan required for the building regs
I forgot to mention it on a quote the other day.

many thanks, Lee
 
I am unsure on ventilation in many areas, in a kitchen i would guess that a fan is ok just on a pull cord or is a humidity stat a requirement , many thanks
 
I am unsure on ventilation in many areas, in a kitchen i would guess that a fan is ok just on a pull cord or is a humidity stat a requirement , many thanks

A humidity stat is not a requirement. An extractor fan is though. It must also extract a certain litres/min. A six inch fan will be sufficent. On the last extension I did I put a 4" fan in and got pulled by the BCO. I managed to get away with it because he wasn't sure what the correct extraction rate was, but I later found out it should be 6".
He wouldn't accept the hob extractor on it's own as a method of extraction. Hope this helps.
 
Right then chaps just to clarify:

The following figures taken from my building regs book.

Mechanical extract ventilation can be operated manually and/or automatically by a controller or a sensor. Fans should not be rated at less than

15 litres/second for a bathroom

30 litres/second for a utility room

30 litres/second for a kitchen where the fan is located within a cooker hood or is not less than 300mm from the centreline of the hob space , is under humidistat control and is located near the ceiling, or

60 litres/second if the fan is located elsewhere in the kitchen.

So as Gaffer says there may well be 100mm fans that extract at the required rate, but keep the specs to hand to prove to the BCO that the fan conforms to building regs!!

Looks like my BCO was using his own rules Surprise surprise!
Hope this helps
 