Right then chaps just to clarify:
The following figures taken from my building regs book.
Mechanical extract ventilation can be operated manually and/or automatically by a controller or a sensor. Fans should not be rated at less than
15 litres/second for a bathroom
30 litres/second for a utility room
30 litres/second for a kitchen where the fan is located within a cooker hood or is not less than 300mm from the centreline of the hob space , is under humidistat control and is located near the ceiling, or
60 litres/second if the fan is located elsewhere in the kitchen.
So as Gaffer says there may well be 100mm fans that extract at the required rate, but keep the specs to hand to prove to the BCO that the fan conforms to building regs!!
Looks like my BCO was using his own rules Surprise surprise!
Hope this helps