Just put a extract fan in for someone fed off lighting circuit. Came to do my testing and found Ze was reading 11ohms :nonod:. Didnt even bother checking anything else, disconnected it and told the client to get DNO out to check. To be honest though it looks like the cowboy who rewired it in the last year or so has put his own BS951 clamp on (It is TNCS) but it looks like its not even touching the lead sheath. I didnt want to get involved with touching that mess.

Whats the best advice in this situation? I am thinking of saying sorry but you will have to leave it isolated until you get the earth sorted and then go back an do my testing and liven it up. Chances are he'll try and worm his way out of paying.
 
Why didn't you bother doing the rest of the testing? You could have done everything except the Zs and then had a much easier time of it when you return to connect and certify the job.

Plus it will be very awkward if you find something else wrong when you do the testing now, that would certainly help to earn you a bad reputation.

Are you sure it's a TNCS?

What did the DNO say when you reported this fault to them?


Sent from my iPad using Tapatalk
 
Why didn't you bother doing the rest of the testing? You could have done everything except the Zs and then had a much easier time of it when you return to connect and certify the job.

Plus it will be very awkward if you find something else wrong when you do the testing now, that would certainly help to earn you a bad reputation.

Are you sure it's a TNCS?

What did the DNO say when you reported this fault to them?


Sent from my iPad using Tapatalk

DNO not been out yet. I have told the customer he needs to get them out. I could nip back tomorrow and do the rest of the testing. Tennant is away anyway so I guess I could get it done. Your right Dave, looking at the state of the install (No idents on MCB's no earth sleeving in lighting, messy in CU) it could well have other issues. I'll check it out in the morning.

Yes it is a TNC-S
 
Last edited:
DNO not been out yet. I have told the customer he needs to get them out. I could nip back tomorrow and do the rest of the testing. Tennant is away anyway so I guess I could get it done. Your right Dave, looking at the state of the install (No idents on MCB's no earth sleeving in lighting, messy in CU) it could well have other issues. I'll check it out in the morning.

So you didn't speak to the DNO yourself? A that really the best plan?
 
However that aside, What I was after is what you would do in that situation. Leave it isolated?

Without the rest of the test results I don't know what I would do!

If the rest of the circuit passes, including the RCD tripping times then I would be happy to rely on the RCD for fault protection in the short term.
 
Without the rest of the test results I don't know what I would do!

If the rest of the circuit passes, including the RCD tripping times then I would be happy to rely on the RCD for fault protection in the short term.

Funnily enough, I did do the RCD tripping times and they were fine. Checked PSC impedance also and that was fine.
 
Just put a extract fan in for someone fed off lighting circuit. Came to do my testing and found Ze was reading 11ohms :nonod:. Didnt even bother checking anything else, disconnected it and told the client to get DNO out to check. To be honest though it looks like the cowboy who rewired it in the last year or so has put his own BS951 clamp on (It is TNCS) but it looks like its not even touching the lead sheath. I didnt want to get involved with touching that mess.

Whats the best advice in this situation? I am thinking of saying sorry but you will have to leave it isolated until you get the earth sorted and then go back an do my testing and liven it up. Chances are he'll try and worm his way out of paying.
If it's got a lead sheath then it's TN-S not TN-C-S.

Sent from my SM-G361F using Tapatalk
 
Did you try getting a Ze directly on the lead?

I did an EICR today where the Ze tested on the sheath was 0.12 ohm and the Ze on the dodgy 951 clamp at its terminal was 0.18ohm


Sent from my iPad using Tapatalk
 
No, my bad. Just what I was thinking I tested at the clamp only. So i'll check the lead tomorrow. I spoke to the client/landlord and it sounds like he got the rewire done on the cheap, no testing etc. My first comment to him was this cant have been tested and he sheepishly told me he didn't get a cert. I'll check the lead tomorrow before he calls out the DNO but if that meters out ok where would I go from there. The 951 shouldn't be on the sheath anyway and now I know its a sh|tty install.
 
No, my bad. Just what I was thinking I tested at the clamp only. So i'll check the lead tomorrow. I spoke to the client/landlord and it sounds like he got the rewire done on the cheap, no testing etc. My first comment to him was this cant have been tested and he sheepishly told me he didn't get a cert. I'll check the lead tomorrow before he calls out the DNO but if that meters out ok where would I go from there. The 951 shouldn't be on the sheath anyway and now I know its a sh|tty install.

Don't worry too much about the value on the sheath, it won't make the situation right either way, I just find it interesting to get as much information as possible when encountering these problems.
If you can get post the reading on the sheath up here I would be interested to know what the difference is.

Better that you call the DNO, then you can actually get your point across rather than Chinese whispers
 

Reply to Very high Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
953
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
539
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi, looking for some advice on what I have seen at my mums house when I took the cover off the consumer unit. 32A breaker, labelled kitchen...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock