T
TPES
When doing your IR tests on a circuit and there coming up low... Just over the 1.0 Minimum what comments are you writing on the certificate to cover your self for any come back in the future?
As far as im aware if its under 2.0 Megohms it should be investigated further. If you haven't already I would split down the circuit and see if you can find what is causing this low reading. From my experience it is better to try and find the fault right away than hope to not get called back. Now although over 1.0 Megohms is acceptable I have also found that there has been some kind of fault on the circuit causing this. Often by dropping of a few accessories I have causing the readings to go back up to more what you would expect.
Ofcourse though if you have already done this you should write in your Comments box on the EIC that ther readings are just over the acceptable limit according to BS7671:2008 and you recommend that the circuit be rewired for preventative maintenance to cause any future nuisance tripping.
Hope this may have helped.
Matt
Like it, like it.
Sounds like a good thing to write in the box,
I've made the mistake of changing a CU in a shop without doing a IR test first, Now the unit has been changed some of the IR tests are low. I also, as you say investigate a circuit with a reading of less than 2.0 megohms, Although to be honest I've only come across this a handfull of times.
I wanted to note on the cert about the low but acceptable tests results, but as the insulation still may deteriate over time it is likely that it is going to fail on its next recommended inspection...
this job was not a great earner and the landlord is a right tight arse and would not of paid for any further time spent investigating or renewing circuits.
I realise i made the mistake of not doing a IR test before i started on the Mains change
Yeah i mean to be honest a full PIR is prob best before the board change. To test for all faults that u may find. However IR tests and a selection of earth loops are what i normally do before a CU change.