Went to a house today that had an aube controller for underfloor heat mat going wrong. Resetting itself. End to end resistance was 152 ohms. Room is about 5x3 metres. Is this indicating damaged heat mat?

Bit of a novice with underfloor. Cant stand it!!

Ed
 
Is there a website for the manufacturer. Might be worth a look and see what they give for a resistance reading for a mat that size
 
Check manufactures instructions for resistance of heat mat for said area (should find it online), been a while since doing underfloor heating but does sound a wee bit high, looked on-line think it should be around 17.6ohms but not sure on value for area and had a few

- - - Updated - - -

Check manufactures instructions for resistance of heat mat for said area (should find it online), been a while since doing underfloor heating but does sound a wee bit high, looked on-line think it should be around 17.6ohms but not sure on value for area and had a few

- - - Updated - - -

Check manufactures instructions for resistance of heat mat for said area (should find it online), been a while since doing underfloor heating but does sound a wee bit high, looked on-line think it should be around 17.6ohms but not sure on value for area and had a few
 
Last edited by a moderator:
love the title

if its under screed then tiles i would have thought your problem would be with the stat
 
Hi,

Just done some Googling. Aube Controller 15A/3450W.

Heat Mat 150W/ Sq M therefore current 2250/230= 9.78A and resistance is 23 Ohms ( for 5M x 3M ). I've never installed this type of heating, so you will probably need advice from someone who has,

Regards.
 
It's under tiles and screed i think. Only 18 months old. Faulty stat i'm sure but resistance felt very high to me.

Which brings me onto a question that feels so stupid i am embarrassed to ask it but i would've thought that larger mat = greater resistance = lower current but this defies logic. I would've thought larger mat draws more current right?!

It seems odd that heating elements in general (toaster, kettle, elec radiator) draw high currents when by their very nature they are high resistance loads - the resistance causes the heat doesnt it?!

Thanks all!

Ed
 
cant be right if you calculate it using ohms law 230 divided by 152 you get 1.513 amps which equals 348 watts which is about a 2 and a half square meter mat at 150w per square meter
 
Which brings me onto a question that feels so stupid i am embarrassed to ask it but i would've thought that larger mat = greater resistance = lower current but this defies logic. I would've thought larger mat draws more current right?!

It seems odd that heating elements in general (toaster, kettle, elec radiator) draw high currents when by their very nature they are high resistance loads - the resistance causes the heat doesnt it?!

Thanks all!

Ed

W=V²/R

Fix V at 230V, plug in a few different values of R and see what happens to the power. All will become clear.
 
Can anyone answer the question i had?! I know low resistance = high current that's why you get for example high reading for prospective fault current. I know all this i learnt it all at college but what i'm saying is surely a bigger mat would be a bigger current (logically) but this implies it is lower resistance than a smaller one! Is this the case? Larger heating elements have less resistance than smaller ones?! Surely the longer/larger the element (assuming same material) will mean less resistance?!?! For example a dead short both at for example 230v between cable of 1000mm2 csa will yield higher current than dead short on cable 1mm2. Surely someone can grasp what i'm groping at here!?!? Thanks!!
 
Can anyone answer the question i had?! I know low resistance = high current that's why you get for example high reading for prospective fault current. I know all this i learnt it all at college but what i'm saying is surely a bigger mat would be a bigger current (logically) but this implies it is lower resistance than a smaller one! Is this the case?
Yes. The larger mat will generally be designed to have a lower resistance.

Larger heating elements have less resistance than smaller ones?!
Yes, for the same power per square meter.

Surely the longer/larger the element (assuming same material) will mean less resistance?!?!
I'm not an expert on underfloor heating, but I think that typically, the "cable" is more complicated than it looks. You'll find that in some cases the line and neutral run the full length of the heating cable and the actual elements are in shorter sections, connected in parallel across L and N. So a longer heating cable just consists of more elements in parallel. The overall resistance will therefore be lower.

Certainly that's how some trace heating cables are constructed.

I'm sure someone who's more familiar with this will correct me if necessary.
 
So larger wattage heating elements are longer rather than thicker basically. Someone said to me they were thicker which confoooosed me. Ok that makes more sense now. Thanks.
 