Just had a call out, no power to house, rewired 4 weeks ago. The culprit was a vphase unit, no power coming out of the transformer and I could not bypass it as the only isolation was the cut out fuse. Thought I better not pull it as its for a local authority and I wouldn't be going back to fix it, the council sparks would.

Has anyone else had much problem with these? I hope I didn't miss something simple! Lol.
 
The firm I work for are subcontracted for the out of hours call outs as the LA sparks apparently can't the arsed to do it haha.
 
Just had a call out, no power to house, rewired 4 weeks ago. The culprit was a vphase unit, no power coming out of the transformer and I could not bypass it as the only isolation was the cut out fuse. Thought I better not pull it as its for a local authority and I wouldn't be going back to fix it, the council sparks would.

Has anyone else had much problem with these? I hope I didn't miss something simple! Lol.
erm - vphase units are not supposed to be whole house VO units, they have an 8 amp continuous, 20 amp peak, and 60amp bypass current rating, so are designed to only be used on a selection of circuits not including any electric heating circuits.

council should get back whoever fitted it to sort it out under warranty - pretty dangerous actually if it had more than 60amps going through it.
 
erm - vphase units are not supposed to be whole house VO units, they have an 8 amp continuous, 20 amp peak, and 60amp bypass current rating, so are designed to only be used on a selection of circuits not including any electric heating circuits.

council should get back whoever fitted it to sort it out under warranty - pretty dangerous actually if it had more than 60amps going through it.

So a pretty pointless bit of kit to install in the first place!!! Even worse when the electrical installer makes a mess of installing them. ...lol!
 
Lol! I've never fitted one before, I've only worked on commercial sized units that reduces the voltage, these are fitted at the mains. I've found they cause tripping problems with older rcd's / rcbo's as they are rated at 240v not 220v.

The vphase unit I looked at had the entire board fed off it, apparently the client was in the shower when the power went off, now I realise why......

I will admit I didn't know it was supposed to be installed this way, but I would of checked the installation guide before I had installed it. It was also about 12 in the night too.. Lol!
 
Lol! I've never fitted one before, I've only worked on commercial sized units that reduces the voltage, these are fitted at the mains. I've found they cause tripping problems with older rcd's / rcbo's as they are rated at 240v not 220v.

The vphase unit I looked at had the entire board fed off it, apparently the client was in the shower when the power went off, now I realise why......

I will admit I didn't know it was supposed to be installed this way, but I would of checked the installation guide before I had installed it. It was also about 12 in the night too.. Lol!

If these commercial units you have fitted, have a rated output of 240 volts, they aren't Voltage Optimisers are they?? ...lol!! They won't as such, have a load operated by-pass facility either, as they will be rated for the premises max demand load!!
 
If these commercial units you have fitted, have a rated output of 240 volts, they aren't Voltage Optimisers are they?? ...lol!! They won't as such, have a load operated by-pass facility either, as they will be rated for the premises max demand load!!

No, the output is 220v at mains and the old rcbos are rated at 240v! :)
 
No, the output is 220v at mains and the old rcbos are rated at 240v! :)

Sorry, my mistake!! It's the old case of not reading twice and answering once syndrome again!! lol!!

I doubt very much if 20 volts is going to make that much of a difference either way to RCD's/RCBO's tripping/sensing characteristics.
 
Sorry, my mistake!! It's the old case of not reading twice and answering once syndrome again!! lol!!

I doubt very much if 20 volts is going to make that much of a difference either way to RCD's/RCBO's tripping/sensing characteristics.

I agree, but taking into consideration volt drop, some of the reading I was getting on sub dis boards were as low as 207v. Old install and VD was must not of been taken into consideration lol!!!
 