UK Warehouse fault help

Hello all, recently moved from installation only in commercial and industrial settings to maintenance in a commercial setting. So far I’ve been managing pretty well with any fault finds I’ve had to do but this one has me stumped, and any ideas would be greatly appreciated.

It’s a large warehouse that take returns of mainly white goods e.g. washing machines, American fridge freezers etc, and attempts to fix the items to sell on at lower costs.

2 weeks ago they lost all power, the main breaker had tripped, as well as 3 MCCB’s in the main LV panel. All 3 MCCB’s were for the “rework bays”, and they are all on an under voltage coil which I assume is being used as there emergency stop in the bays. As well as the trips in the LV panel, a random socket circuit in the office tripped off, 2 bay door panels blew up and needed replacing, and essentially all outside emergency bulkheads need replacing due to a short created on the circuit, which was such a nightmare to track down we just decided to replace them all.

Today the exact same thing happened, main breaker tripped, the 3 MCCB’s and the socket circuit. This time no lights or bay door panels were destroyed though. Both times the staff have gone and reset all the breakers without issue before I get there. Everytime they’ve turned the breakers back on the outside flood lights have flashed continuously for some time too.

My only theory at the moment is that an appliance they have plugged into one of the reworks bays has created a fault current high enough to take out the main breaker as well as the UV coil. However I feel like I’m clutching at straws.

Any ideas what could be happening or where to start trying to figure out what’s causing this?
 
Possibly a phase loss an undervoltage coil will almost certainly trip on a phase loss.
 
Possibly a phase loss an undervoltage coil will almost certainly trip on a phase loss.
Possibly a phase loss an undervoltage coil will almost certainly trip on a phase loss.

What could cause a phase loss that isn’t upstream?

Loose connection on the main incoming?

Could a large inrush current causing a voltage sag do it?

I initially thought it may have been a phase loss due to the first time it happened being during a storm.
 
Possibly Floating Neutral.

If it's a 3 phase supply a loose / missing Neutral on the incomer in the L.V panel or anywhere upstream including on the DNO supply.

If it's a single phase supply it's possible the Neutral is failing in the DNO supply before it enters the building.

Clues are when single phase items go pop, due to Phase to Neutral being over voltage and undervolt coils tripping due to Phase to Neutral being under voltage.
 
Hello all, recently moved from installation only in commercial and industrial settings to maintenance in a commercial setting. So far I’ve been managing pretty well with any fault finds I’ve had to do but this one has me stumped, and any ideas would be greatly appreciated.

It’s a large warehouse that take returns of mainly white goods e.g. washing machines, American fridge freezers etc, and attempts to fix the items to sell on at lower costs.

2 weeks ago they lost all power, the main breaker had tripped, as well as 3 MCCB’s in the main LV panel. All 3 MCCB’s were for the “rework bays”, and they are all on an under voltage coil which I assume is being used as there emergency stop in the bays. As well as the trips in the LV panel, a random socket circuit in the office tripped off, 2 bay door panels blew up and needed replacing, and essentially all outside emergency bulkheads need replacing due to a short created on the circuit, which was such a nightmare to track down we just decided to replace them all.

Today the exact same thing happened, main breaker tripped, the 3 MCCB’s and the socket circuit. This time no lights or bay door panels were destroyed though. Both times the staff have gone and reset all the breakers without issue before I get there. Everytime they’ve turned the breakers back on the outside flood lights have flashed continuously for some time too.

My only theory at the moment is that an appliance they have plugged into one of the reworks bays has created a fault current high enough to take out the main breaker as well as the UV coil. However I feel like I’m clutching at straws.

Any ideas what could be happening or where to start trying to figure out what’s causing this?
I assume from the above that the undervoltage supply is derived from the mains supply and not a separate DC battery charger in which case the three MCCB's will always trip out on undervoltage as soon as the main MCCB is isolated/tripped. This maybe giving you a false impression.
Have you checked the thermal and magnetic settings on all the MCCB's, it could be a discrimination issue.
You said that the main MCCB trips out when the socket circuit trips, it could be the magnetic trips on the main MCCB are set too low in which case it will also trip when the socket circuit trips along with the three MCCB's which will trip due to "undervoltage".
Do you know why the socket circuit keeps tripping is it due to overload, short circuit or earth fault?
 