Discuss Water damaged PYRO in flat in the Australia area at ElectriciansForums.net

T

TPES

Hey all what do you think to this..

Ive had a call out to 2 faulty lights in 2 different bedrooms.

Bedroom 1, the lights work, but when the customer changes the lamps they blow very quickly.. (so he says)

Bedroom 2, the lights dont work at all, the customer has tried new lamps but nothing.

All cores are black.

Further investigation in bedroom 2 revealed the circuits are installed using MIMS cable. The feed is at the fitting with switch wires down to the switch.
I removed the switch to find no voltage at all on either core. After time belling out the cores i determined what was what.
When i removed the light fitting i found alot of water damage to the cores, This had been caused to the flat above being flooded over 6 months ago. See the attached photos

In the photo you will see..

Feed in / N in
Feed out / N out
COM down to switch
Switch Live

From what i have figured there is no voltage at the switch as the COM down to the switch has been damaged/broken.

I tested this by linking the Switch live into the Perm feed, this will give me voltage at the switch, but when the switch is switched there is no voltage back up at the light. Only one of the cores seems to be intact.

I need to write a report on this of the dangers and whats needs to be done to rectify the fault. what would you write?

Has anyone come across this before? What do you think?
I'm sure it will need a re-wire
 

Attachments

  • 200902121220_131.jpg
    89 KB · Views: 89
  • 200902121220_133.jpg
    90.7 KB · Views: 70
  • 200902121221_134.jpg
    86.9 KB · Views: 81
  • 200902121221_135.jpg
    105.3 KB · Views: 74
hi did you do a continuity test on all cores i could be reading your post wrong but if you
just put a live on the switch and switched on how do you know its not just a faulty
switch i just cant see you loosing a line on pyro through water damage without getting a short
try a insulation test between lines and lines and earth (outer sheath)
 
Last edited:
hi did you do a continuity test on all cores i could be reading your post wrong but if you
just put a live on the switch and switched on how do you know its not just a faulty
switch i just cant see you loosing a line on pyro through water damage without getting a short
try a insulation test between lines and lines and earth (outer sheath)
agree with the old dog here,you really need to be separating all your wires and meggaring(ins restance test) all your cables,to sheath(earth).You will then have readings on each core then to back up your report,this will enable you to mark up your colours also.I couldn't make out from your pictures clearly,but it would appear that the installer has used 3 core,giving a possable spare if you could use the sheath as the sole earth?? (or are they pots with an earth tail?) It is possable for cores to break but usually due to excessive wiggling rather than water
 
I have a similar problem (pls read my own thread)

Tell me.. how did you word your report and also the pics do look like it was caused by water damage. Did you reccomend complete rewiring to the whole property? what sort of remedial work did you have to do in the meantime


Hey all what do you think to this..

Ive had a call out to 2 faulty lights in 2 different bedrooms.

Bedroom 1, the lights work, but when the customer changes the lamps they blow very quickly.. (so he says)

Bedroom 2, the lights dont work at all, the customer has tried new lamps but nothing.

All cores are black.

Further investigation in bedroom 2 revealed the circuits are installed using MIMS cable. The feed is at the fitting with switch wires down to the switch.
I removed the switch to find no voltage at all on either core. After time belling out the cores i determined what was what.
When i removed the light fitting i found alot of water damage to the cores, This had been caused to the flat above being flooded over 6 months ago. See the attached photos

In the photo you will see..

Feed in / N in
Feed out / N out
COM down to switch
Switch Live

From what i have figured there is no voltage at the switch as the COM down to the switch has been damaged/broken.

I tested this by linking the Switch live into the Perm feed, this will give me voltage at the switch, but when the switch is switched there is no voltage back up at the light. Only one of the cores seems to be intact.

I need to write a report on this of the dangers and whats needs to be done to rectify the fault. what would you write?

Has anyone come across this before? What do you think?
I'm sure it will need a re-wire
 
I have a similar problem (pls read my own thread)

Tell me.. how did you word your report and also the pics do look like it was caused by water damage. Did you reccomend complete rewiring to the whole property? what sort of remedial work did you have to do in the meantime

The pictures look like BESA boxes in concrete, with a bit of TLC they should be OK.
Why recommend a full rewire? It would be a nightmare unless you’re one of these plastic trunking cowboys. The insurance isn’t likely to fall for your little scam.
 

Reply to Water damaged PYRO in flat in the Australia area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
784
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
556
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
373
Hey all :-) Hope its chill that I'm here asking questions, I just inherited this old decrepit place in NSW (Australia) and went to wash my hands...
Replies
2
Views
819
Hi, I am looking to convert a 2 way light into just control by single switch. I have searched and looked for similar questions here, and found a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock