Biff, dude, bow out if you can't answer the question. I have tried to be polite and humour you but it seems my efforts have been wasted.

I am trying to get a sensible answer to a sensible question, but you seem intent in taking the thread off topic.
 
well, not really. There has been, as far as I can determine, no 'breakdown of core insulation.'

And the fuse was not blown. Ballast input 230v, output 230v.

If you can recall, I was asking a two part question.

1. What can cause a ballast to 'fail' while still putting out 230v?
2. Is it true that a ballast should put out 500v before settling back to 230v (as I have been told)

Please bear in mind that replacing the ballast resulted in the satisfactory lighting of the lamp.

xx = respect blud.
 
I've just had a thought,

I'll test a working ballast first chance i get this week, and IR test a faulty one and then I'll get back to you.
 
You wont be able to measure the 500v, it happens quickly when the lamp ignites. Power is switched onto the fitting and the ballast builds up its magnetic field the starter or ignitor breaks the circuit and causes a surge from the ballast which ignites the lamp. The ballasts second job is to limit the current as it build ups its field it opposes the current, hence them also being called a choke.

Measuring 230v at the output doesnt mean much at all it could of broke down inside but still be high resistance. It could be a sort of phantom voltage.

On reading that back it's not the best explanation but its the best I can do while having a poop with people trying to get in the cubicle!!...

Search Google for a better explanation with im sure diagrams of how ballasts work.
 
Cheers for that Brightspark. I had a fair idea about how they work from when I was at college. I guess the ignitor is part of the ballast unit then. I will try to get hold of some manufacturers information to confirm this.
 