Hi guys I really need some help on this question. semi enclosed fuses are located in a distribution board where Ipf was measured and recorded as 4ka. What code would be given during a periodic and does and what is the associated regs number for it?

THANK YOU
 
Rockingit

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
3,942
What makes you think that a value of 4kA is a danger? Also - is that a figure derived from 1ph or 3ph nominal or actual measurement? What are the withstand values on the cpd's??

I'll grant it would be an unusually high value for a standard 230v domestic but on a 3ph supply doesn't sound unreasonable at all.
 
OP
justtryingtolearn
Reaction score
1
What makes you think that a value of 4kA is a danger? Also - is that a figure derived from 1ph or 3ph nominal or actual measurement? What are the withstand values on the cpd's??

I'll grant it would be an unusually high value for a standard 230v domestic but on a 3ph supply doesn't sound unreasonable at all.
Hi, I really appreciate your reply. its a single phase and a actual measurement. It's a question that's on one of my 2391 question papers and I haven't got a clue. That's actually all the information that is given.

So on a single phase would you class this as a fi code?
What makes you think that a value of 4kA is a danger? Also - is that a figure derived from 1ph or 3ph nominal or actual measurement? What are the withstand values on the cpd's??

I'll grant it would be an unusually high value for a standard 230v domestic but on a 3ph supply doesn't sound unreasonable at all.
 
P

pc1966

Esteemed
Arms
Reaction score
5,984
Reg 434.5.1 cover this.

BS 3036 can (I think) be found in 1kA, 2kA and 4kA breaking limits so all are a problem if you have a high capacity supply, though as above I suspect a PFC or PSSC of 4kA and above is quite rare in domestic boards.

The usual BS88 supply cut-out fuse might help you if it is 63A as that limits your peak current so with 4kA PFC (symmetric RMS amps) you max is 3kA peak so would be OK for a 4kA rewirable fuse, but if the supply fuse is larger it won't help. End of circuit faults ought to be OK as your R1+R2 may limit the PFC, or your 13A fuse will do it, but not for wiring faults near the DB.

Unless you know that the particular style of fuse is as high as 4kA and the supply use is 60A/63A then I would put this as C2 code as potentially dangerous.
 
OP
justtryingtolearn
Reaction score
1
Reg 434.5.1 cover this.

BS 3036 can (I think) be found in 1kA, 2kA and 4kA breaking limits so all are a problem if you have a high capacity supply, though as above I suspect a PFC or PSSC of 4kA and above is quite rare in domestic boards.

The usual BS88 supply cut-out fuse might help you if it is 63A as that limits your peak current so with 4kA PFC (symmetric RMS amps) you max is 3kA peak so would be OK for a 4kA rewirable fuse, but if the supply fuse is larger it won't help. End of circuit faults ought to be OK as your R1+R2 may limit the PFC, or your 13A fuse will do it, but not for wiring faults near the DB.

Unless you know that the particular style of fuse is as high as 4kA and the supply use is 60A/63A then I would put this as C2 code as potentially dangerous.
 