F
falcon0310
went do call out tonight
tt supply and old elb rcd not working
240 oms on earth rod
getting belt from water no eath bonding but good ra test
450 oms on sockets
10 mm to eath rod
2 young children in house
long short was sorrey cant do anthing but do rewire, next door just had rewired with no 100 ma rcd ! just 30 ma
Old wylex boards cables taped up one way board under the sink cables clipped to banister I can't spell
450 oms on sockets
10 mm to eath rod
.............. and you left it in this state????
I understand where you're coming from but what do the test results say? If they test out ok then you might get away with a new CU and some rerouting.
I'd be doing a bit of testing to find the fault and as a minimum change elb to working rcd
Guy turned back on and sent email didn't charge him as spent 2 hours looking what can you do but tell them the facts ?..
Yes tested it with robin and kewteck wouldn't even trip on ramp test
I'm confused .com ........ From your OP: tt supply and old elb rcd not working So is this device Current Operated, or Voltage Operated?
- - - Updated - - -
An old VOELCB won't work in the same way as an RCD mate, two totally different things.
Awww ... you're too quick for me. :(
450 oms on sockets
10 mm to eath rod
Oh Dear!! ...Basically hasn't got a clue what to do to resolve the problem, so suggests a rewire!!​