B

Buzz-light-bulb

I've looked through previous threads and still slightly confused as to what actually Is exporting pme, can some one give me a quick breakdown to help me on my way.
 
generally, you don't export PME, you extend the equipotential zone. i.e. extend the PME earthing to an outbuilding. the only drawback is that if there's extraneous parts in the outbuilding, you need a bonding conductor no less than 10mm.
 
I've looked through previous threads and still slightly confused as to what actually Is exporting pme, can some one give me a quick breakdown to help me on my way.
when i read the title `what is exporting one`..

i thought it was going to be about toilet humour...
 
generally, you don't export PME, you extend the equipotential zone. i.e. extend the PME earthing to an outbuilding. the only drawback is that if there's extraneous parts in the outbuilding, you need a bonding conductor no less than 10mm.

Does the 10mm bonding conductor have to be connected directly at the origin met or can it be connected to the extended consumer unit , if this is the case cannot see what all the confusion is about, thanks tel always there to help a man out on the front line
 
Does the 10mm bonding conductor have to be connected directly at the origin met or can it be connected to the extended consumer unit , if this is the case cannot see what all the confusion is about, thanks tel always there to help a man out on the front line

Of course the 10mm bonding needs connecting at the original MET as well as at the extended CU!!
 
Yes the extended cu will obviously be connected to the origin met, so what I am trying to say is instead of running a separate 10mm back to the origin, it can just be connected to the extended cu.
 
Can't understand why anyone would convert it to TT which has be posted in previous threads
 
Can't understand why anyone would convert it to TT which has be posted in previous threads

You'll keep the earthing and bonding functions completely separate. Might be useful if you have high neutral currents due to unbalanced loading and lots of extraneous parts in both buildings.
The cost also might be a consideration.
 
Yes the extended cu will obviously be connected to the origin met, so what I am trying to say is instead of running a separate 10mm back to the origin, it can just be connected to the extended cu.

say you are feeding a garage with a 6mm 3 core. the 3rd core ( and possibly the armour as well ) will suffice as cpc. but if you have extraneous parts, a separate 10mm bonding conductor needs to be run from the MET. this is because the min. size for a bonding conductor on PME is 10mm.
 
Yes the extended cu will obviously be connected to the origin met, so what I am trying to say is instead of running a separate 10mm back to the origin, it can just be connected to the extended cu.

If you have extraneous metalwork/pipes you have 3 choices. ... You can run in 3 core 10mm SWA, or run in a 10mm separate bonding conductor, or be totally foolish and convert to a TT system!!

The 10mm incorporated core or separate bonding conductor runs between origin MET and extension CU's EMT. A 10 mm bonding conductor is then taken from Cu's EMT to the bonding position of the extraneous metalwork/pipe!!

This is all Very Basic Stuff were talking about here!!
 
Can't understand why anyone would convert it to TT which has be posted in previous threads

Im currently TT'ing 2 containers as its industrial and the incoming supply characteristics would require me to run a seperate 50mm earth with my 4mm swa .... this is obviously a cost issue in my case a its cheaper to isolate the earth at the load end of the swa and rod the system .
 
Im currently TT'ing 2 containers as its industrial and the incoming supply characteristics would require me to run a seperate 50mm earth with my 4mm swa .... this is obviously a cost issue in my case a its cheaper to isolate the earth at the load end of the swa and rod the system .

Out of interest wot makes it warrant a 50mm earth cable for you're main protective bonding ?? Just curious
 