mine in redSSorry I've just re-read the op.
Replacing one pendant for 5 down lights is a MWC and must be to 17th standards. As long as your new cables are beyond 50mm etc etc you don't need to supply rcd protection. yes you do. it's a bathroom. RCD required.
Sorry for any confusion before.
Just had an interesting "discussion" with a fellow spark. Job was/is to replace a single lighting pendant in a first floor bathroom (loft above) with five IPX5 downlighters. Cables clipped to top side of 50mm roof trusses. Board only has RCD covering three ring mains and no spare way on this side of the board. Switch drop is between two sheets of plasterboard with a two inch gap and is not being modified.
RCBO or not for the amended lighting circuit?????
Regards
mine in red
The switch is existing. Does the rest of the circuit come under the 50mm requirement. I would RCD it, but it is an interesting question.
"Switch drop is between two sheets of plasterboard with a two inch gap and is not being modified."
Rcd/rcbo needed just because of the switch drop.
Pendant in a bathroom ? really.
IMHO this is a simple yes or no question to the RCBO.
Is the modification being undertaken in a bathroom? - Yes - then RCBO is mandatory IMHO