OK GUYS!!!!! pull the switch drop out fit pull switch alter lighting for spotlights now theres no requirement is there if you want to disect it.
Had one the other week, batton holder with incandescent lamp in zone 1 right next to the shower head. No chance of easily moving due to the metal conduit encased in solid concrete, very nice 50's build. Managed to find an IP rated holder that fitted straight onto the conduit without modification.Pendant in a bathroom ? really.
yes ther eis requirement for RCD. 701.411.3.3 applies. end of.
it's a question of how far you can go before bringing the work up to current regs. if a simple like replacement. i.e. changing 1 fitting for a new single fitting, then i would agree, no RCD required, but modifying the circuit by fitting 5 downlighters is, IMO, a major enough change to warrant complying with 7671(2011).Are the lights within zone?
Do we have to provide rcd extra protection for existing cables whilst doing an extension of a circuit? (add an extra socket to any circuit out of zones and not used for external use)?
We all agree to put it on an rcd but show me a reg that says that we have to supply rcd protection for an out of zone circuit that your adding on to? Let's remember that this is not a new install, its a modification to an existing install. As said before, interesting question for a Sunday night.
Bang on tel.
Too many so called sparks now try to get away with fitting as little as possible. until the claims start coming in and then finding no MWC was issued so mr sparky has no leg to stand on.
quick cash job at the time but its the shortcut jobs that come and bite ya later.
No its not like for like as I explained in my other post.
What is the actual question here?
Out of zones in a bathroom, does an addition to a lighting circuit need to be on an rcd?
Yes we would all like to put it on an rcd BUT what do the regs say?
Changing the characteristics of a circuit by changing one light pendant to 5 down lights? No. (only over current).
Nobody has quoted a reg that explains this situation. Telectrix regs is for new installs as per 7671 2012 and not for the hard wired cables at the time they were installed. No offence Tel but no one has come up with a definitive answear yet.