While I was at college I was constantly told to fill the hole by one tutor in particular :nonod: , I took this as meaning double the cable into terminations thus 'filling the hole', Now out in the real world the majority of work im coming across seems to be lacking in the hole filling dept, Just wondered what everyone's stance was on this subject?
 
Something we were allways told as well, double over & fill the hole for better screw contact.
 
Got to be honest I dont always do it, but try whenever poss, 1.5 lucks wimpy in termination without being doubled.
 
I normally double the CPC, not L and N. Is there any right or wrong or is it just personal preference?
 
:lol: know what you mean Alex & I sometimes "Forget" as well.
 
Last edited by a moderator:
From what I've seem out and about, the older install's tend to have more doubled over cables, maybe a sign of the times - cant drop a cu in in half an hour if your doubling cores, (cant belive I just said that-sure somebodys gunna come on an tell me otherwise)
 
I always do but on a recent inspection assessor told me that some people say doubling over actually goes against the regs as it puts stress on the core. The thought being that it could break and the screw could only be tight on the return part of the bended core but not on the incoming bit....Made me laugh.
 
I only double the core if I can't get a satisfactory connection with the unbent wire in the terminal. Even then more often than not I'll use a bootlace ferrule crimp instead.
 