The only analogy I can come up with is, Your out driving your car,an incident occurs in front of you, your brakes fail and you think, never mind I have the airbag to save me, hang on a minute, I didn`t put one in because it was extra work that I couldn`t be arsed to do, bollox! Bang!
 
Last edited by a moderator:
Maybe.....but then they'd have to jackanory their R1+R2 ,Ze and Zs results in order to make it look right on the cert.......you dont really think that sort of thing goes on do you?


No Comment!! lol!! Though from what i've been seeing lately, nothing much surprises me anymore!!! Probably will even think it doesn't matter, i have a max of 1667, so i've covered my arse!!
 
Another possible scenario:

Circuit installed years ago, fuse used to provide 5 second disconnection time, Zs complies with that OK.

Maybe come to change the CU, new circuit (<32A) now needs a 0.4sec disconnection time, Zs is now too high.

What do you do?

This question is not directed to anyone specifically!
 
No Comment!! lol!! Though from what i've been seeing lately, nothing much surprises me anymore!!! Probably will even think it doesn't matter, i have a max of 1667, so i've covered my arse!!

i'm just itching for the day someone comes on the forum with a Zs of 1668 ohms lol
boy , we'll nail his --- to the wall big time.
;-)
 
Last edited by a moderator:
The Electricians Forum Guide to Circuit Design
==================================


Step 1
=====

Fit rcd.






there is no step 2.


I'd be grateful if admin could make this a sticky , saves all that faffing about with regs books and equations.



;-)
we`ll have no Electrical Trainee stuff in here thank you very much....:wink_smile:
 
Another possible scenario:

Circuit installed years ago, fuse used to provide 5 second disconnection time, Zs complies with that OK.

Maybe come to change the CU, new circuit (<32A) now needs a 0.4sec disconnection time, Zs is now too high.

What do you do?

This question is not directed to anyone specifically!

Fit 20amp mcb, or if a ring with a high load split into 2 radials and fit 2 x 20amp mcbs (assuming complies with that zs figure)
 