Hello. I have ordered two LED Strip lights from Amazon to replace two fluorescent fittings, one of which does not work. After recent electrical work being carried out i am left with wiring as shown in the attached images.
My question is, which wires should i be using to connect the new fittings when they come. Many thanks
 

Attachments

  • 20240518_171411.jpg
    20240518_171411.jpg
    322.7 KB · Views: 110
  • 20240518_171430.jpg
    20240518_171430.jpg
    288.2 KB · Views: 93
Is that circuit isolated? Presumably you have removed light fittings before taking those pictures and whoever did the recent electrical work did not leave it in that poor condition?

In the first picture the 2 brown conductors joined together are permanent live, the blue conductor and the grey conductor identified as blue are neutral, the black conductor identified as brown is switched live.
The switched live must be be disconnected from the two neutral conductors as that is creating a short circuit which will be potential really dangerous if switched on.

In the second picture the two red and one brown conductor are permanent live, the black identified as blue and the grey (which needs identifying as blue) are neutral, the two blacks identified brown are switched live.

In both pictures the green/yellow conductors are earth which must be properly connected together, and to the new fittings if they have an earth terminal, before the circuit is energised.
 