This week I've done a small job in a retail outlet and for the same people a small job in their home. Chatting to the client it transpires their lodger is a sparky (not sure where) and he's planning to change the fuseboard in the house, plus he did the electrics in their retail unit.

Not quite sure how this happened but the client phoned the other guy and we were discussing the 2 jobs he's done/doing:

Me: I'm just doing fault finding at the house before I can do the certificate (almost no IR between N-E)

Him: Why are you doing a certificate?

Me: to cover the "repositioned" light switch, and during the testing I identified the fault so I isolated the outside lights so the RCD would hold

Him: Oh

Me: Are you going to fit a RCBO board?

Him: Why?

Me: Its a very old house with multiple changes/additions inside and out and I think its the best way to go.

Him: I've got a dual board suppose I could convert it

Me: Just to let you know I've also done a small change to a radial socket in the shop, I've labelled DB1 and DB2 to help the customer.

Him: Why did you do that?

Me: Because if there were any labels, they must have fallen off and there wasn't any certificate to refer to so I've made the set up a bit more obvious for the users.

Him: Silence

It later transpired that even though the retail unit was done over a year ago they haven't received any certificates, and he can't sign work off. Apparently there were a few chaps on the retail install.

Don't think he'll be buying me a beer in the near future!
 
i was working at a packaging factory this time last year, a new office within the factory has been built and i found a CU buried in the wall so much i had to chisel the plaster away to get the lid off, one of the circuits was feeding 3x over sink 20L water heaters and 3x double sockets marked 'for fan heaters only', this was supplied from 2.5mm twin & earth radial, in a stud wall with no insulation, on a C32 MCB!!!
i asked the manager which idiot did this, he said "one of the production engineers"
when i found said engineer he wouldn't tell me whether he was qualified or not and made an excuse to get away!
 