Hi can anybody help? Why can I not find in the regs or OSG the correction factor for multi-core cable with an ambient temperture of 25 degrees? I can only find thermosetting or thermoplastic? What is multi-core classed as, I am busy working out a cable calc for my level 3 course with not much luck.
Cheers.
 
Last edited by a moderator:
So are you saying that thermoplastic is multicore, because could you not class thermosetting as multicore also?
 
no , im not saying that in the slightest ??? :-/
its down to the type of insulation , pvc or xlpe.
 
Ok, I see, then the cable calc I have to work out is not specific enough then, as it asks for the correction factor for a multi-core cable at an ambient temperature of 25 degrees.
Thanks for that, I appreciate it mate.
Cheers Derry0178
 
Ok, I see, then the cable calc I have to work out is not specific enough then, as it asks for the correction factor for a multi-core cable at an ambient temperature of 25 degrees.
Thanks for that, I appreciate it mate.
Cheers Derry0178

Biff has already given you the calc you require.

Look on page 325 (Regs) Table 4B1
 