call out to RCD trip . as soon as downstairs lighting MCB is closed, RCD ( dual RCD board, ) trips. L/E reading 0.02 Meg. logical approach, start at first light, split circuit and proceed from there. open 1st rose, all 3 L conductors twisted together and stuffed under 1 screw . OUCH. fault is downstream. OK, onwards. 6 fittings later, several terminations remade, end up in downstairs loo. FCU for fan and light, fuse removed. fault still there. open FCU. cables so short had to snip at terminals. get FCU to where i can see it properly, arced and burnt through plastic between Lin terminal and earthing bar. fault now cleared. extend cables with through crimps, heat shrink, new FCU. close up ceiling roses and switches. IR test at CU. reconnect, close up. 4 hours to find a simple fault. ( mind you, the house was full of junk, right obstacle course. also, customer is family friend, so gave a generous discount on normal rate.