S spikey Mar 26, 2009 #1 hi chaps,done a ze test on a tns supply,got a reading of 0.18 ohms.i was expecting around 0.8.can anyone shed some light on this.many thanks
hi chaps,done a ze test on a tns supply,got a reading of 0.18 ohms.i was expecting around 0.8.can anyone shed some light on this.many thanks
S Spudnik Mar 26, 2009 #2 Did you carry out a true Ze ie with main bonds disconnected? If so, 0.8 is the maximum, so anything under is fine.
Did you carry out a true Ze ie with main bonds disconnected? If so, 0.8 is the maximum, so anything under is fine.