hi, just been to a Call-out, mobile home site. one homeowner has had a faulty socket replaced and the electrician who did the job, quite correctly filled out a MWC, problem is his Zs reading was 51.2 ohms. now, the supply comes approx. 100yards from the cut-out ( which is boxed on the supply pole) in 2 core 6mm SWA, using the armour as earth ( circa 1960's). I checked his readings with MFT and got 49.5ohms, then measured Ze at the cut-out, 0.22ohms PME system. think it's pretty clear, it's the resistance of 100yds of armour that is the problem. the home has a 30mA RCD , front end 16th ED. so my query is: do i leave well alone, or dis. PME and convcert home to TT. which will hopefully make the installation comply. replacing the cable is not a option, considering that half the park will have to be excavated.
 
From my understanding, the 30mA RCD means that the 51.2 ohms reading isn't a problem.
 
50Ω is a big reading - is it worth looking for a corroded high resistance joint at one end or the other that can be re-terminated?
 
Due to the RCD it can be 1667 ohms and still activate within the required time.
 
2-core swa using armouring as cpc should give a resistance of about 1 ohm over 100m, probibly should be worth a look for corrosion somewhere on the joints!
 
also it should,nt be on pme dont think csa of swa will be 10mm a minimum requirement of pme.
 
points taken. will check both end connections 2morrow. told home owner there's nothing to woory about as she has RCD. with regard to your post, nick. DNO converted to PME with that cable already in place. so, as per my orig. post, do you think i should convert the home to TT and dis the home end of the armour?
 
I'd make the glands off again if there is enough movement to do so and see what if that makes any difference to the readings.
 
i forgot to mention. the cable is not glanded. the armour is earthed at both ends with jubilee clips. suspect oxidation, but it started to p*** down so that,s first thing to check tomorrow
 
Ah ok in that case I would get the clips off and give it a dam good wire-brushing or going over with emery paper to clean up the faces and see if that helps.
 
You should carry out an R1R2 test to confirm a low continuity ....which there obviously wont be.As the others have said almost certainly down to poor terminations of the SWA and corrosion.
 
that's the plan. however, if i can't get the reading down to an acceptable value, do i TT it and get an even higher reading. also, from the MWC done by the spark who did the socket replacement, the RCD is listed as 100mA, so i will check this and replace with 30mA if so.just a bit confused as to why he's done a MWC for a like for like socket replacement.
 
Not sure on the TT front, I guess if you TT and RCD it then the earthing will be correct, rather than it being a poor condition PME installation that is covered by an RCD...if that makes any sense?

Probably not, but it sounds right in my head!
 
Not getting what you mean by a 'mobile home' site.

Would this not be classed the same a caravan site, and therefore not be allowed on a PME(CNE) system?

Are you sure the SWA is not just earthed at the supply end - and the 'mobile home' installation is TT'd as it's supposed to be......this would make more sense of your reading:)

Nothing wrong with PME coming in as main supply to park, but shouldn't be run to caravans/mobile homes!

100mA up-front RCD also points to it being a TT installation.


Just my thoughts.:)
 
Last edited by a moderator:
it's not exacly mobile homes as in caravans. it's those prefab homes like a large static. but set on bricks. called park homes. and the swa armour is providing the earth
 
it's not exacly mobile homes as in caravans. it's those prefab homes like a large static. but set on bricks. called park homes. and the swa armour is providing the earth

OK, we'll go with this for now.

The thing I would be more concerned about, rather than the Zs of the 'prefab home' installation(as this is RCD protected), would be this:

How are the services entering the 'home' (extraneous), bonded to the MET.
Bearing in mind that the MET, technically, is at the cut-out.

Unless I'm mistaken, where PME conditions apply, the Main Bonding Conductor has to be sellected in relation to the supply neutral conductor (up-stream of the cutout), and I don't think the armour of 6mm 2-core will suffice - I might be wrong.
It certainly isn't good enough with a resistance of 49.28 ohms.:)
 
yuo're right there. i assume that originally it was tns, from MET is 16mm to jubilee clip on SWA, then approx 80m to home where earth taken off SWA. Manweb, or whoever it was called then, converted this mess to PME some years ago. at the moment all i am concerned about is making it safe. will discuss options for improvement once i,ve done the best i can with what's there
 
Last edited:
It certainly sounds like the jubilee clips might be your main problem - you've got high resistance joints somewhere.......is it not possible for you to gland both ends into an appropriate enclosure.

The 16mm should be alright at the cutout end - you could use same size at 'home' end.

Just need someone to confirm the 'copper equivalent CSA' of 6mm 2-core SWA.


then approx 80m to home where earth taken off SWA.

Does 6mm work out okay for 'volt-drop' over 80 meters?
 
Last edited by a moderator:
there is a guide that gives swa csa,s.i dont think 6mm will comply.if you tt the supply at meter position you will comply as long as swa csa is 6mm
 
volt drop depends on load current.but 6mm is pretty tight.might sqeeze in on a 32amp mcb
 
more info tomorrow. her indoors gone to bed!
 
DSCF0168.JPGgone back today, traced back to here. took pic after removing 2 bare 2.5 earths from jubilee clips. fine mess. love the socket directly wired to tails! ripped it all out. TT'd it. got to return to relace twin socket with RCD socket. got rained off
 
and we get accused of ripping people off to put things right when the kettle has been working fine for years!
 
nick, seen the pic? that is not a problem? nother prob. the 16mm incomer is from the pole cut-out. assumed that the 2 6mm were load side. i terminated the 16mm into an isolator and re-inserted the fuse so as to restore power to the 4 homes i had dissed. wallop! one of the 6mm is now live. caught it with my elbow, OUCH. seems there are 2 feeds into this bag of trticks. made safe when rained off.
 
Last edited:
think that the live 6mm is looped from the home which is the main problem as regards earthing. and the 16mm was originally for another purpose long lost in the past. as of today, i have terminated the 16mm into a " garage box" 2 pole isolator, 40A MCB ( for home) 16A MCB (for RCD socket local) and made the live 6mm safe. tomorrow morning will hnopefully not be ******* down and i can trace the other feed.
 
Last edited by a moderator:
Right, sunny day, further investigation shows that although the rat,s nest and the home are supplied from the same cut-out, the home is not supplied from the mess in the pic. this morning i have TT'd the home and dissed the armour at the home end. Ze measured at178ohms, within the 200ohm max. the home owner's electrician has been informed by me that he must replace the 100mA RCD with 30mA. He is asking me for a cert. on the work i have done, and i am thinking EIC, limitations to be stated as install TT earthing only. don't think MWC will do. does anyone know if there is a specific cert. for work outside the home?
 
I know what comes next. the guy is niceic so will say a TT system has to be under 100ohms. brb says 200. already feel like telling him to go forth!
 
I know what comes next. the guy is niceic so will say a TT system has to be under 100ohms. brb says 200. already feel like telling him to go forth!

Why do you want to do that? Sounds like he does his job properly and if everyone did you wouldnt have that mess there.
As far as I am aware my mate whos in the NIC says they work to 200 ohms and has no idea where you got 100 from.
You need to complete and eic and state the change to TT on that particular sub circuit only unless youve changed others. You will need to record the method of measurement, measured resistance ( with rod disconected from met if using method 2) type of electrode and location. 178 is still pretty high though if it was me I would try a longer rod or different position to try and get it down. If its too high there may not be enough prospective current to trip breakers. It sounds like youve got a bit on there sorting that mess out. Have fun!!
OH dont forget your supply characteristics will have to be recorded seperately because I presume that isnt TT.
 
Last edited by a moderator:
Why do you want to do that? Sounds like he does his job properly and if everyone did you wouldnt have that mess there.
As far as I am aware my mate whos in the NIC says they work to 200 ohms and has no idea where you got 100 from.
You need to complete and eic and state the change to TT on that particular sub circuit only unless youve changed others. You will need to record the method of measurement, measured resistance ( with rod disconected from met if using method 2) type of electrode and location. 178 is still pretty high though if it was me I would try a longer rod or different position to try and get it down. If its too high there may not be enough prospective current to trip breakers. It sounds like youve got a bit on there sorting that mess out. Have fun!!
OH dont forget your supply characteristics will have to be recorded seperately because I presume that isnt TT.

Agree that 178ohms is high, especially for a winter/wet ground reading, but it is a pscc that will take the breakers out in this case and an earth fault of more than 30mA that will interrupt the supply via the rcd and 1667 ohms will still give that.
Oh and welcome to the forums :)
 
it.s a nightmare. the supply cable is daisy chained feeding 5 homes,not mapped out properly, at each, armour is jubilee clipped with fly leads.so could be poor connections. going to try and trace it from source, reading ELI and PSCC at each. prefer to get the original earthing up to scratch than rely on TT. as said, at 178, it's a tad high. in response to you, fathom, i,m not knocking the home owner's spark for doing his job right. it's just that myself and the site owner are stuck in the middle, dodging cloudbursts trying to rectify the problem. bearing in mind that we have to interrupt the supply to all 5 homes while working and he's sitting in the warmth writing out condemnation notices.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
Ze & Zs-- unacceptable readings
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
35

Thread Tags

Advert

Thread statistics

Created
telectrix,
Last reply from
telectrix,
Replies
35
Views
8,849

Advert

Back
Top