Worzol99 to be fair we all get stuck and daft questions that we are 99% sure on but thats why we come on here. we just need quick clarification. Would sooner someone ask what seems a "silly" question and get a correct answer than be afraid to and do something dangerous.
 
Worzol99 to be fair we all get stuck and daft questions that we are 99% sure on but thats why we come on here. we just need quick clarification. Would sooner someone ask what seems a "silly" question and get a correct answer than be afraid to and do something dangerous.

True, especially if an individual isn't aware that there may be more than one DB involved in an installation.
 
Thanks ipf I've come on here just for a double check before and get met with sarcasm and poor attitudes. I enjoy banter but sometimes certain members make you feel small for trying to ask for help in order to do a proper job.
 
Thanks ipf I've come on here just for a double check before and get met with sarcasm and poor attitudes. I enjoy banter but sometimes certain members make you feel small for trying to ask for help in order to do a proper job.

Sorry for the upset but a bit of thought, search or book use, would be the easiest option.
 
Thanks ipf I've come on here just for a double check before and get met with sarcasm and poor attitudes. I enjoy banter but sometimes certain members make you feel small for trying to ask for help in order to do a proper job.
Good Point well made as I get the same impression. I am right with you on this one. There are a lot of guys out there who believe they are gods gift to this forum and the electrical industry, who as you say only offer indifferent attitiudes, sarcasm and nothing of value.

Least we forgot we have at all times asked silly questions and still do today. We learn something new everyday and always continue to, and may possibly learn at times by asking a question no matter how stupid it may appear.

If we cannot on this forum offer any help sincerly to others then we are all the poorer for it.
 
It is really very straight forward
Ze the the External Impedance of an istalllation and should be measured at the following points.

Domestic: At the incoming/supply side of the main switch in DB
Larger installs: At the incoming / supply side of the main Switch on Sub Main panel.

I am of the belief that it should be termed Zdb be a lot clearer and easier all round.
Also on test sheet a tick box verifing if MEC was able to be removed safely from MET for said Ze [Zdb] test.
 
There should be no confusion at all on this one.

There is only one Ze at the installation, no mater domestic commercial industrial or whatever, and it is at the main incomer of supply, all the rest will be Zs Or Zdb, no matter how many boards you have, it is still not external is there? You may think, when you test at sub main DB, it seems like it is Ze, but it is Ze to that board only, but it is still in consumer installation, is there?

And don’t matter how you call the test at that particular DB, it is still the same test. Isolate that board first, and test the loop between incoming L and E, that’s all.
 
Last edited:

Reply to ZS at DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
609
Yes, probably overthinkig, thanks.
Replies
6
Views
490
I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
145
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
1K
OLDBOY
O
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks