Evening all, can one of the Guru's of the forum help me please ? I have been watching my mentor wiring up UFH the past couple of days, and now its my turn in the morning :ack2: under his supervision. I have taken it upon my self to get a head start and was wondering if this proposed diagram would work correctly? I have very little experience with contactors so would like some guidance.

Contactor help.jpg

Thanks in advance, If I don't reply tonight I will in the morning.

Ellis
 
All looks good apart from your netutrals, the feed to switch the contractor is from a 13amp supply yet the neutral is from the 32amp supply.
 
Thanks Dillb, I'm hoping to get this sometime soon. So if I replace the A2 with the 13A supply's neutral the switch over will work ?

Thanks :)
 
Yes, it will work the way have drawn it, but you would then have the problem if a shared neutral.
 
Ok I think I have it now :) always keep the neutrals relevant to their supply. Thanks for correcting me mate much appreciated.
 
i can. he's supplied the A2 form the other neutral is all.
 
Can't see your picture Marvo :(
A1 and 2 are the live and neutral from the thermostat. 1 and 2 are the incoming 32A supply the contactor is switching and 3 and 4 are the corresponding switched live and neutral to the heat mats.
All as you would expect.
 
I tried to view it on the tapatalk app, just looked on the pc and it worked, thanks again for the corrections and the updated drawing.
 
Can I ask why the neutral is switched as well? Most of the contactors I see are just switching the supplys
 