O
Octopus
So the back ground to the situation.
Gas /boiler mate replaces boiler and relocates it by about 2 meters.
Old cabling to boiler :
L, N, E and SL
New cabling to boiler:
L, N, E and SL - so cable just extended.
This is where it gets interesting:
The tank is a Megaflow, it has a tank stat, the SL from the tank stat goes to a Megaflow thermal cut-out connection (rather than back to the boiler & Megaflow have told me NOT to bypass it). At the thermal cut-out the connections are also to a Megaflow 2 port motorised valve (well actually its a Sunvic SZ 2302)
Here is a link showing the thermal cut-out etc wiring (about 1/2 way down).
http://interpart.partsarena.eu/System/DATA/Dx/DS1/installation/2978/I48-2978/I48-2978.htm
My problem is that the grey at the auxiliary switch is PL and whether the switch is open or closed it remains a PL connection. As the motor turns the valve there is a click and the voltage drops momentarily. I tried to call Sunvic technical but they go home at 4.30 so 4.55 was a bit late
So the Orange remains PL rather than SL and thus the boiler has a SL which is pretty much PL all the time.
The Gas/boiler man has changed the valve twice!
So can I please call on the collective knowledge of you good chaps, to point out the error in my thinking/understanding.
Tin hat well and truly on!
Here are some photo's of relevant bits:
I'm not familiar with the sunvic valve. Normally closed from the cylinder thermostat should go to one side of the thermal cutout, other side of cutout should go to the brown of the valve. Grey of the valve is permanent live, blue neutral and the orange is the switch live to the boiler which also is connected to the pump. I take it there's another valve? If there is, is it a two port or 3 port valve?
As above - Grey is PL, and Orange SL, if Orange is PL also then i suspect a duff micro switch, but seen as its been changed twice id be surprised its that.
Has the gas man changed the body of valve maybe at fully open the spindle is jamming ,and the valve not returning and so not breaking the micro switch.
Something strange there Murdoch.
The Megaflo manual shows a 2 port valve yet the drawing you've posted for the SZ 2302 would seem to indicate a 3 port valve because it has an input for hot water and central heating.
You need to talk to the plumbers to find out if the changed anything other than move the boiler.
will check but I'mm 99% sure the boiler has a pump in it.
there will still be a pump in the system for the Heating even if the hot water Is gravity fed which if it is then it's a bit naughty of the plumber as it should of been upgraded to fully pumped when the boiler was changed under part L. Is there only the one valve?
2 valves. the CH works ok when i disconnect the SL from the water!
So, if it's a 2 port valve then it looks like the feed from the tank stat (S/L) goes to the brown, and orange to the boiler. You do not connect the grey.
so it sounds like it's not gravity and is an Splan with a high limit/themal cutout as its unvented. So when HW is turned on, on the programmer the common on the cylinder thermostat should become live, cylinder thermostat is below the water temp then normally closed on cylinder thermostat should be live, normally closed should then go through the the thermal cut out and power up the brown of the valve, valve should then motor round and close the micro switch between grey (permanent live) and orange switch live. So if the valve is staying open and closing the micro switch then the body of the valve could be stuck but the plumber should pick this up when replacing the head or the brown is picking a feed up from somewhere as it must be wired wrong as the heads been replaced a few times it sort of rules out it being a dodgy head.
With the juice of and the orange and greys of valves removed is the switch closed. If it's open and there's a live on the orange could there be link passing a feed to valve at junction box, maybe the boiler pump arrangements have been changed. Ie over run and boiler is feeding outgoing side of micro switch. Just a thought could be Pish. Not the brightest when it comes to various boiler controls.
Is that a fudge or should the head be swapped to the SZ 2351?
The home owner knows her house was built by bodgit and scarper so its the latest of her issues swallowing her money...
The home owner knows her house was built by bodgit and scarper so its the latest of her money swallowing her money...
I think it's a fudge Murdoch, though it should work.
The actuator is for a gravity fed system but if you wire it as the drawing and ignore the CH side of things it should work ok.
SL to brown, orange to boiler. There's no need to worry about the grey, that just brings on the pump for the CH in a gravity system. You've got another 2 port valve for that.
Definatly not. Orange becomes live from the permanent live of the grey which should come from pl from boilers pcb. But from murdoch op it hasnt been wired with a 5c to boiler L,N, PL, SL, cpc. So it may be an older boiler which may not specify sl fed off pl on pcb so may have grey linked to pl in wc. It does sound like a Dodgy head apart from you say "wetpants" has changed the valve twice. Are you sure you werent getting back feed off ch orange.? Maybe fresh look at it will serve you well next visit, not a nice job last call of day!
I've just googled the valve and Andyb looks like he has it spot on. The valves not a conventional valve where grey is permanent live. Brown of the valve connects to normally closed of the cylinder thermostat and orange switched live to boiler/pump. The orange of this valve will also be commoned with the orange of the other valve. As this valve is usually for Gravity HW and pumped central heating I'm not sure if having the oranges from both valves together will affect by back feeding the valve if it does then it would be easier to replace the sunvic with a standard Honeywell two port.
It doesn't have a permanent live, it's the wrong valve.
You are correct in what you say if it was the correct valve, but there is no grey/orange S/l P/L for that valve.
Look at the drawing Murdoch posted in picture 3.
If you look you will see that when you put the switch live to brown the orange becomes live to feed the boiler. Like I said it's for a gravity system.
Well that's a bit of an interesting one!
Those valves are a bot of a pita sometimes, I've encountered them before and nearly lost the plot trying to work them out. Assuming it's the one I tikka it is!
I've had a bit much cider to be any help now, but I'll have a proper look at it tomorrow and consult my notes on boilers.
Having slept on it Murdoch I think you should change the actuator or complete valve. Any demand for heating will open HW valve by backfeeding through the boiler.
If you use a Sunvic actuator it should be a straight swap with no plumbing involved.
The Sunvic SZ2302 is a spring return valve, supplied with the Megaflow unvented cylinder and must be fitted.
It's a safety device to cut off the heat source if the cylinder goes overtemp.
The Gas /Boiler man should be G3 qualified to fit an unvented cylinder and should know not to replace the valve with anything other than a 2 port spring return.
Not sure I understand this comment!
The valve can be replaced with any normally closed Spring return valve. Doesn't have to be sunvic but might be easier as the body won't have to be changed and that means no draining down.
The Megaflo thermal cutout is the safety device Snow, not the valve which is fed through the cut out. It can be any 2 port spring return valve but it needs a nc switch which the SZ2302 does not have.
It's the wrong valve and should be replaced.
Looking at the 3rd picture in Murdoch's op it's the Sunvic SZ2351 that's needed if you want to stick with Sunvic, though as I said, any spring return valve with a switch will do.
I'm going to call Sunvic this morning so will post what they recommend.
Thanks for all the input so far - I'm glad it wasn't straight forward after all.
I did get a call off a member who spotted the issue pretty much straight away - I won't name them unless they want to come clean....
lol I think his name starts with H....
UPDATE:
Sunvic Technical : 01698 810945 (who were excellent)
Have confirmed that the valve in place isn't correct (I think I knew that) and that it needs to be swapped for the SZ 2301 (valve normally closed, switch normally open). The body is the same so just a "simple" case of swapping the head.
Happy days!
UPDATE:
Happy days!
UPDATE:
2 "happy" texts today :
1st from customer
2nd from plumber (he fitted the replacement head last Friday).
A least this is now well and truly sorted!
Ok, I admit it, I'm stumped......
Central Heating Systems
Tags Tags
None
Octopus,
Octopus,