I had an electrician come to do a safety check at my property that I let out last week and he has recommended that remedial work should be done at a cost of 2,100 pounds, These are:-
Upgrade of eco 7db
Upgrade of 2 x circuits to RCD protection
Install of isolation point for underfloor heating
identification of points where required
Fusing of points
Enclosure of exposed wiring - these are wires that are not in trunking
Investigation of supply wiring and condition of main isolator and repair
Retermination of required points
cable enclosures
Nothing listed but the sub total is 1,750 plus VAT comes to 2,100
Is that a lot! I last had a test done five years ago, true the wire of the economy 7 is in a situation which is not assessable, however he wants to run a wire from it across the lounge and into the kitchen!
But the amount seems excessive and it is through the Agents who manage the property for me.
Any suggestions would be very helpful.
Many thanks Surreygirl
It wasn't clear whether that was what the "electrician" would charge £80 or whether the agent would charge that... if the later... how much is the guy doing the inspection going to make?
£80 for an estate agents EICR seems to the "norm" around here. I guy called Jamie seems to do all the estate agents around here. (source: a couple of estate agents who told me we were trying it on with our price!)
Well the Agent charged me 240 pounds for the test which failed.
However I managed to get hold of he original electrician who fitted the underfloor heating and also issued a safety certificate and he is at least going to sort the problem out with the lack of an isolation point and lack of trunking for the wires! and also an electrician recommended by someone on this site is going to look at the cable that he cannot test!
And how long was the "electrician" there?
Less then an hour as I was there at the same time. It is only a studio so not much to test and as for checking the cable that runs behind the wall I didnt see him take out any box to see the cable or even test the economy 7 it is too far up and needs a step ladder to get to it and he certainly didnt take out the main fuse box in the kitchen. he did note though that the underfloor heating did not have an isolation point which was useful and so the electrician who fitted the underfloor heating is going to put one in and also trunk the grey wires. He knew it was a rental property. He also gave me a safety certificate for his work and all the electrics.
he might just as well have sat in his van and made it up. n EICR in less that 1 hour? bloody joke, and £240 is a complete rip-off for the time he was ther.
That is what I thought but he come through the Agents and when I questioned his suggestions about the cable - from what you guys had told me when he came around again the Agent came along too and told me that no on had every complained about him before! - However 1,600 pounds to run a cable that he was unable to check due to it having a connection seemed on the high side to say the least and that is even if there is a connection to be tested. Because on here you told me he should be able to test the cable the Agent then came back to me and said it was the connection that he couldnt test but that is if there is a connection! and anyway going on the length of the 3 meter rule the connection should only be about 2 feet away so I do not see how he could could no test it and as I said he certainly didnt test the cable whilst I was there.
Anyway a lovely person on this site has recommended a "spark" to me so he is on the case!!
Ditch the electrician and also the letting agent, that's ridiculous.
1 hour, no steps, I can't understand what he means regarding the cable behind the wall and he did not go to the consumer unit if I understand correctly.
He did go to the consumer unit with me because he needed to know where it was and he showed me where the cable would run from but as it is directly behind my lounge/studio wall and the wiring runs directly in a straight line to the economy 7 main fuse box in the lounge and at the top of the cupboard there would be about 11 feet or wiring because my consumer unit, which is about 2 ft along the outside wall, so that takes two feet of off the 12 ft to the kitchen - if you follow my drift - so any connection either end - and it is probably the kitchen end -would only be about 26 inches from either the main meter or the fuse box in the kitchen and as he intends to remove the one in the kitchen there would be a great big hole so I do not know why he would be unable to test the connection. That is, if there is one! And the same for the economy 7 main fuse box in the lounge. If he removes that he could test the connection. Testing the connection is why he has said he needs to put in a new cable. Testing the connection is what came out after a lot of prompting from me from what you guys told me to ask!
But at no time did he test the cable running from the main meter to the flats main fuse box in the kitchen!
Also I agree about ditching the Agent because when I got there all the work which was supposed to have been carried out like a new shower and a cooker hood had not been done and that was supposed to have been done months go and also this fiasco with the electrician.
Sorry SG, I can't understand why he needs to re run the economy 7 cable (if that's what you are saying)
Did he take the cover of the consummer unit? did he take any sockets or switches off the wall or inspect any of the lights?
Well in his report he says "upgrade of eco 7 DB"
He could not really test that as he could reach it you need a step ladder as it is right up the top of the wall and in a cupboard.
The further down the report he says
Investigation of supply wiring and condition of main isolator. This is where he said he could not test the main wiring, but then when one of you chaps said he must have the equipment to be able to test it, his reply was that he needs to test the connection, he said there was a 3 meter rule and that the join would be too far in for him to be able to test! and that it was the connection that he needed to test and because he could not get at it he wanted to run new wiring through my lounge up on the top of the lounge wall which I quite categorically do not want. I cannot imagine what a great big cable would look line running along the wall. Not to mention is it necessary!
He looked at the fuses and told me the underfloor heating had the wrong fuses in and so switched them off and told me that the tenant must not use the underfloor heating until it had all been updated.
You need a lot of equipment to undertake a PIR, steps is just one. you cannot undertake an inspection in most cases, including this case, without a pair. Also, if he could not access the DB how can he say it needs replacing?
Please do not let him or anyone for that matter run a cable through your lounge. Unless I'm totally misundersting this, he's having a laugh.
I know you've been asked before but could you not scan and post the report?
reading that, i gave up after counting 4 Bull Sh1ts. (from the sparks, that is, not you).
as previous posts, bin both the agent and the so-called electrician.
Yes I am going to upload his report. Just got to set the printer up because - do not laugh - poetic justice or something!- when I turned on the computer when I got home last night the electrics went and I can only use a few sockets without it tripping! so need an electrician here now. Am just about to sort out the printer so will upload when I get it up and running.
I agree. I felt that I was being taken for a ride that is why I posted on this forum to get down to the bottom of it and of course I have lost all confidence in the Agent now and I will be looking into changing them in the near future. I have got a "sparky" going in who was recommended by one of you chaps and as I said the original electrician who put in the underfloor heating is going to put in the "isolator" and trunk the grey wiring.
Just put some paper over the names.
It is in Pfd form at the moment. I am trying to upload to the computer as electrics went last night along with my tower so am just sorting out the lap top and the printen and the I can upload my copy with names blocked out.
I will get that done as soon as I can.
You are all lovely xx
I'll kick it off... how can he make the statement "Inconsistent resistance values for ring final circuits" when he doesn't appear to have actually tested/recorded them?
Given it's a studio flat, are there too many points of utilisation for him to count and record?
It's unlikely you'll get identical results for the various insulation resistance tests as he has recorded, unless you max your meter out (so I very often write >999 in all IR test results).
Max disconnection time for the shower circuit... it's a final circuit so it's max disconnect time should be 0.4s, not 5.
Can't see what's wrong with the fusing of the under floor heating... the breaker is 16A and it's wired in 2.5mm... nothing wrong with that. And at the other end I wouldn't expect anything else, just a connection to the under floor heating controller.
The rest of it, difficult to say without seeing the installation, but I stand by what I've said already... he's a chancer, trying to extract as much money from you as possible and I suspect he's in cahoots with the agent. Ditch them both.
Rather than spending time writing it all out again, I will just say I agree with everything SparkyChick has said.
Well that is what I thought. I had my suspicions especially when his response that they - meaning the Agents - "just" take the money out of the rent. With the emphasis on "Just"! That made me sit up and think.
Thank you for taking the time to read the report. I have some one going in to look at the electrics for me, next week hopefully! Someone on here gave me the details of an electrician near to me, so that is a relief.
I also think that the Agents are dodgy as there have been a few things on a smaller scale that I have questioned and then the strange answers to questions I have put to them which you all kindly told me to ask!
Such as not being able to test the cable and then when I questioned that on what you have said they then come back to me and said it was the connection that he couldn't test etc etc etc!!
Rock on surreygirl
Hanpton wick
Business Name
none
Am I being taken for a ride?
surreygirl,
Pete999,