Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
 
Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
Regulation BS7671 544.1.2 Without quoting verbatim, bonding is to be applied to the consumers side of the meter where practicable, with 600mm of the meter outlet union, or point of entry to the building, if the meter is external.
Was the Electrical work certified by the Electrician, main bonding should be mentioned on the certificate, but then again if Kevin the Kitchen fitter did the Electrics I would doubt very much if any such certificate was issued.
 
Hi just after some advice
Some friends just had a new kitchen fitted, but as far as I can tell there is no main water bonding, I believe that it has to be about 600mm from the ground or there abouts.
If it’s not there will the kitchen need to come out to fit one
Where are you in the UK?
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east

Your profile suggests that you are a fully qualified electrician.

This is very basic stuff.

You wouldn't use a multimeter to test, test the pipe back to the MET.
 
youmeasure between your MET (main earthing terminal and the copper pipe on your side of the stop cock. if resistance value is > 22 k Ohms, then it's not extraneous. if i't < 1 ohm, then it's bonded anyway.
 
It was done by Phil the kitchen fitter.
The pipe coming in a don’t no, without moving the kick board which has been sealed in.
I thought the main earthing you needed was the water supply and the gas, unless the house was all in plastic pipes.
How do you test with a multimeter if there is no cable??
In yarm in the north east
Anthony, firstly it's not earthing water and gas, it's called main bonding.
Sounds like your Kitchen Fitter didn't know much about Electrics, so there was no certificate then? In order to test to see if the pipes have been bonded a Multimeter will not be applicable
These two videos will go some way to explain.
 
You can test between a local earth connection i.e. a socket outlet and the water service. Provided it's verified that this has a good MET connection. Saves getting the wander lead out!
 
You can test between a local earth connection i.e. a socket outlet and the water service. Provided it's verified that this has a good MET connection. Saves getting the wander lead out!
Sorry Willy, don't agree with your suggestion, far to many Parallel earth paths to make an appraisal as to whether the pipe is bonded.
 
Anthony, firstly it's not earthing water and gas, it's called main bonding.
Sounds like your Kitchen Fitter didn't know much about Electrics, so there was no certificate then? In order to test to see if the pipes have been bonded a Multimeter will not be applicable
These two videos will go some way to explain.
Not seen John Ward before - Very clear and comprehensive presentation!
 
The earthing system has not been stated. If it's TNCS then testing to a local socket or other earth is not sufficient to verify compliance. If the service requires bonding then it will have to be in 10mm minimum which can only be verified by a combination of testing and visual inspection.
 