So I have had an enquiry about a large open plan call center with around 150 desks.

Rented office space, each desk has at least 1 pc with 2 monitors.
There is also all the other IT equipment you would expect in a big office.

The office sockets are fed from 2 x bus bar trunking runs under the floor.
Each of these is fed from a 40A RCBO via swa cable.

There are many floor mounted boxes each with 2 x twin sockets that are plugged in to the trunking system that then run the office equipment at the desks. Singles in flexible conduit, steel spiral type.

Problem is the RCBO’s are tripping at random intervals, sometimes in the day and sometimes overnight.

I have logged the current on each circuit for 5 days and found max load in the region of 30A on both circuits with no peak before current drops to 0 (breaker tripped)

All equipment has been recently pat tested and has a clean bill of health.

The obvious diagnosis is that a cumulative leakage from all the IT equipment is tripping the RCBO.

There are 2 ways I am considering dealing with this,
OPTION 1

Split the trunking into 4 runs instead of 2 fed from 4 x 40A RCBO’s
This will probably fix the issue and is the cheaper and quicker option.

OPTION 2
Change the RCBO’s to Standard breakers.
Mark the trunking runs along there length with warning about lack of rcd protection.
Change all the socket outlets to rcd sockets.

This is my preferred option, it would still provide protection to all outlets.
A fault on one socket won’t black out half the office but be confined to that socket only.

What are people’s thoughts?
In my mind, both options comply with regs.
The trunking is not accessible without lifting the floor.
 
RCD sockets would giv ethe best resistance to nuisance tripping and represent the best option for the customer.
However if they want the cheapest option rather than the best then splitting across 4x feeds might work. However there is no guarantee that this will eliminate the nuisance tripping.

I don't see any need to label the trunking if it isn't fed via an RCD, it doesn't need it and you wouldn't normally expect to find it fed by rcd
 
So I have had an enquiry about a large open plan call center with around 150 desks.

Rented office space, each desk has at least 1 pc with 2 monitors.
There is also all the other IT equipment you would expect in a big office.

The office sockets are fed from 2 x bus bar trunking runs under the floor.
Each of these is fed from a 40A RCBO via swa cable.

There are many floor mounted boxes each with 2 x twin sockets that are plugged in to the trunking system that then run the office equipment at the desks. Singles in flexible conduit, steel spiral type.

Problem is the RCBO’s are tripping at random intervals, sometimes in the day and sometimes overnight.

I have logged the current on each circuit for 5 days and found max load in the region of 30A on both circuits with no peak before current drops to 0 (breaker tripped)

All equipment has been recently pat tested and has a clean bill of health.

The obvious diagnosis is that a cumulative leakage from all the IT equipment is tripping the RCBO.

There are 2 ways I am considering dealing with this,
OPTION 1

Split the trunking into 4 runs instead of 2 fed from 4 x 40A RCBO’s
This will probably fix the issue and is the cheaper and quicker option.

OPTION 2
Change the RCBO’s to Standard breakers.
Mark the trunking runs along there length with warning about lack of rcd protection.
Change all the socket outlets to rcd sockets.

This is my preferred option, it would still provide protection to all outlets.
A fault on one socket won’t black out half the office but be confined to that socket only.

What are people’s thoughts?
In my mind, both options comply with regs.
The trunking is not accessible without lifting the floor.
Just a thought, have you measured the EL from each work station? and what is the cumulative EL causing the RCBO trip? again a thought that you may have to reconfigure the wiring method, could be you have far too many WS per circuit.
 
My thoughts on the trunking are as follows.
It is basically a long run of sockets,
There is nothing stopping someone buying another floor box with standard sockets and plugging it into the trunking.
 
My thoughts on the trunking are as follows.
It is basically a long run of sockets,
There is nothing stopping someone buying another floor box with standard sockets and plugging it into the trunking.

No there isn't, but a person who does that without considering the need for rcd protection beforehand is pretty much guaranteed to ignore any label you have stuck on the trunking.
 
Got to go and do some work for a bit.
Thanks Pete for your thoughts so far
I will have a look this evening and try to get my head round peoples responses.
 
agree with davesparks. option 2 IMO. RCD is not required. to cover your arse you could provide a written RA.
 
No there isn't, but a person who does that without considering the need for rcd protection beforehand is pretty much guaranteed to ignore any label you have stuck on the trunking.
Might pay you to have a look at 7.5 through to 7.6 in the OSG Page 86 to give you some food for thought, this also gives you Regulation number to read, I haven't bothered to look myself but it may be that busbar trunking is not the way to go for IT equipment, I don't know to be honest, I do know however IT circuitry can be a right pain, worth a look at the OSG and BS7671 543.71 201, 203, 204, 205.
201 figures 7.5.3, 543.7.2 hope the info helps.
My last office install was suggested that It must be done as per the install you have.
I changed that after consultation to 2 work stations per radial, in Plastic Dado trunking, 24 work stations in total 20A 30mA rcbos never had any trouble after that change either all wired as 7.5.3 OSG
 
Last edited:
Would be good to get clarification on 531.3.4 in the 18th which now seems to exclude the use of RCD sockets to BS7288
 
Might pay you to have a look at 7.5 through to 7.6 in the OSG Page 86 to give you some food for thought, this also gives you Regulation number to read, I haven't bothered to look myself but it may be that busbar trunking is not the way to go for IT equipment, I don't know to be honest, I do know however IT circuitry can be a right pain, worth a look at the OSG and BS7671 543.71 201, 203, 204, 205.
201 figures 7.5.3, 543.7.2 hope the info helps.
My last office install was suggested that It must be done as per the install you have.
I changed that after consultation to 2 work stations per radial, in Plastic Dado trunking, 24 work stations in total 20A 30mA rcbos never had any trouble after that change either all wired as 7.5.3 OSG

Eh? What's that got to do with my point that labels about RCDs are a waste of time?
 