Do you have reason to doubt your tester?High Ze on a tns supply. It’s 1.48 ohms. Weird as I did a Ze here 4 weeks ago and it was 0.50.
Do DNO come out for a Ze that high what is likely to happen when I call them?
Thinking of going home to double check tester is working ok at home before I call them.
Could be a dangerous assuption to make as technically you are leaving an installation with a known fault that could result in the premises losing it's earth connection some time in the futureIt’s all 30ma rcbos so it’s not unreasonable for it to be left on in my opinion.
Presumably you are not using a no-trip low current test?Thinking of going home to double check tester is working ok at home before I call them.
I call the DNO quite a few times a year with earth faults on one occasion the external earth fault on the property I was working on was actually found to have left half the properties in the street without an earth.Definitely worth letting the DNO know, they will be pleased to receive the info. In a similar case (albeit lower readings of about 0.55 to 0.62Ω on a TN-C-S) I spoke with the client and explained the situation with them, and got their agreement to give their contact details to the DNO.
I meant it wasn't unreasonable to leave the property till it could be fixed by the DNO as it had Rcbo and the Ze was 1.5 so it would not be that different from a TT.Do you have reason to doubt your tester?
If you did a Ze 4 weeks ago and you now have a reading that is 3 times higher you could have a developing external fault I would certainly call the DNO and report it as the supplied earth Ze is now higher than is allowed
Oh So I should of turned off the neighbours power too while we wait 2/3 days for the road to be dug up. They would love that.But what if the neighbours don't have RCDs?
A TT has an earth rod that you can inspect and verify it's condition with a TNS earth fault you wouldn't know if the flaky earth would stand up to a high fault current so there is a differenceI meant it wasn't unreasonable to leave the property till it could be fixed by the DNO as it had Rcbo and the Ze was 1.5 so it would not be that different from a TT.
The 2 DNO's where I'm based generally work on a 2 hours to site response when an earth fault is reported and if a dig is required it is done that day so you have guessed wrongI guess you'd turn the power off for 2/3 days in this case then as its a dangerous assupmtion?
Well you might have a looped supply so the earth fault could be in the neighbours propertyOh So I should of turned off the neighbours power too while we wait 2/3 days for the road to be dug up. They would love that.
It wasn’t a guess it is what happened. They came out within 2 hours but said they are too busy too dig up the road so it will take 2/3 days till it’s done. So you’d leave elderly people for 2/3 days with no power in there house?A TT has an earth rod that you can inspect and verify it's condition with a TNS earth fault you wouldn't know if the flaky earth would stand up to a high fault current so there is a difference
When I find faults like that the call to the DNO is in straight away