I assume there are 30ma rcds / rcbos fitted ?I have an overhead supply coming in to the property with a PME , there are two Consumer units with 100ma Wylex RCD's as main switches. Why 100ma ?
100mA are great for lighting circuits, if it is a split load board use a 30mA as the second main switch.
There are no RCBO's or 30ma RCD's, that was the reason for my question, given that this board is around 15 yrs old I'd have. expected a 30ma RCD main switch.Why not?
If you have circuits to protect with flexibles or extension leads, you could use 30mA RCBO's and cure nuisance tripping of the entire board.
25amp for ring final circuits please.
20amp for 4.0mm sequentially wired.
There are no RCBO's or 30ma RCD's, it may have previously been a TT but I could see no sign of an old earth rod outsideI assume there are 30ma rcds / rcbos fitted ?
Was this previously TT earthing ?
There are no RCBO's or 30ma RCD's, and its not a split board, so I'll probably change it in the near future100mA are great for lighting circuits, if it is a split load board use a 30mA as the second main switch.
Yes, I'm going to change it, I was wondering why it was a 100ma as opposed to a 30ma411.3.4 requires that, within domestic (household) premises, additional protection by an RCD with a rated residual operating current not exceeding 30 mA shall be provided for AC final circuits supplying luminaires.
Arguably, the greatest risk on a lighting circuit is somebody accidentally stuffing their fingers into a live socket whilst changing a bulb.Why does a lighting circuit require a 30mA RCD?
I'm afraid that BS 7671:2018 requires that all lighting circuits without exception are protected by a 30ma RCD/RCBOWhy does a lighting circuit require a 30mA RCD?
No, I'm afraid notI assume there are 30ma rcds / rcbos fitted ?