is this an eicr fail

EICRs do not fail they are either satisfactory or unsatisfactory.
What departures are you seeing?
 
We cant tell just by looking at the picture... it could be a rats nest inside that.

Did you get an EICR done, and they have given it an unsatisfactory?
We need the actual remarks made by the examiner, and possibly photos of what each remark refers to.

At the moment, No RCD/ No SPD protection would be a C3... but there may be other items they have "failed" it on
 
We cant tell just by looking at the picture... it could be a rats nest inside that.

Did you get an EICR done, and they have given it an unsatisfactory?
We need the actual remarks made by the examiner, and possibly photos of what each remark refers to.

At the moment, No RCD/ No SPD protection would be a C3... but there may be other items they have "failed" it on
Its quite neat inside for something that age, eicr has not been done yet but the "maintenance manager" has said that he has been told it needs replaced which means replacing 49 of them .
The flats are used as serviced accommodation the original air bnb I suppose,built in 2000 and as far as I know nothing has been added or extended to the original wiring except a change of light fitting here and there.
Its a lot of money for something that may not need replaced
 
The report will hopefully explain why it needs replacing, perhaps lack of 30mA RCD protection (this is just an example). You can then pop it up on here and we can take a look and give our opinions.
 
The report will hopefully explain why it needs replacing, perhaps lack of 30mA RCD protection (this is just an example). You can then pop it up on here and we can take a look and give our opinions.
There hasn't been a report yet the maintenance manager has just told us they need replaced
 
well, one one hand, an EICR performed by a reputable company may say they are fine for continued use, but on the other, if these are rented out units, it may be in the best interests of safety that they do get replaced.

A general maintenance manager cannot say one way or another without testing it properly
 
It is irrelevant if they are rented it is just a dwelling. You Code the absence on this that and t'other as necessary.
 
It is irrelevant if they are rented it is just a dwelling. You Code the absence on this that and t'other as necessary.
yes. you're right... but i did say they MAY want to make it as safe as possible.

Hypothetical situation, EICR performed, Outcome satisfactory with a bunch of C3's... No work is done to improve, as none is deemed "necessary"... Accident happens, landlord is questioned as to why it happened... "Well, the EICR said it was almost safe"
 
It sounds to me as if someone has made a 'corporate decision', possibly in the light of lack of RCD protection, that it would be safer, less hassle, and easier with maintenance and EICR's, to replace them all. That is in the gift of the owners/managers, and given their legal liabilities, seems to me quite prudent.

It may be their thinking that the cost of replacing the lot in one go would be recoverable, over time, through the 'management fees' the residents pay, whereas there would be more difficulty getting individual residents to pay for ad hoc replacement or repair of something they would regard as the owners responsibility!

For what it's worth (to save me typing any more) here's a little more bumf copied from the interweb 🤔

The MEM Memera 21 consumer units and circuit breakers were manufactured primarily from 1982 until the early 1990s, when they were superseded by the Memera 2000 series. The Memera 21 range was built to comply with BS 3871 (Part 1: 1965). This standard governed miniature circuit breakers (MCBs) in the UK before being replaced by the European standard BS EN 60898 in 1994.
 
yes. you're right... but i did say they MAY want to make it as safe as possible.

Hypothetical situation, EICR performed, Outcome satisfactory with a bunch of C3's... No work is done to improve, as none is deemed "necessary"... Accident happens, landlord is questioned as to why it happened... "Well, the EICR said it was almost safe"
If it was deemed safe when it was installed and nothing has changed then it isn't any less safe than it was.

Any installation could be made safer.
 
well, one one hand, an EICR performed by a reputable company may say they are fine for continued use, but on the other, if these are rented out units, it may be in the best interests of safety that they do get replaced.

A general maintenance manager cannot say one way or another without testing it properly
Bingo Answer. It can be non compliant to the current regs on a test cert. They obviously couldn't be installed today, but the commercial element means RCD protection will almost certainly be required. Its not dangerous, its just old.
 
Had a similar job couple of years back, 6units though not 49 where identical boards by look of it, that were deemed Satisfactory on EICR (by another company, albeit with a long list of Recommendations C3's) but landlord said tenant safety was paramount and wanted them upgraded to include SPD/RCD etc so total replacement was best way forward.
We just did the remedial works.
 