Its quite neat inside for something that age, eicr has not been done yet but the "maintenance manager" has said that he has been told it needs replaced which means replacing 49 of them .We cant tell just by looking at the picture... it could be a rats nest inside that.
Did you get an EICR done, and they have given it an unsatisfactory?
We need the actual remarks made by the examiner, and possibly photos of what each remark refers to.
At the moment, No RCD/ No SPD protection would be a C3... but there may be other items they have "failed" it on
There hasn't been a report yet the maintenance manager has just told us they need replacedThe report will hopefully explain why it needs replacing, perhaps lack of 30mA RCD protection (this is just an example). You can then pop it up on here and we can take a look and give our opinions.
yes. you're right... but i did say they MAY want to make it as safe as possible.It is irrelevant if they are rented it is just a dwelling. You Code the absence on this that and t'other as necessary.


If it was deemed safe when it was installed and nothing has changed then it isn't any less safe than it was.yes. you're right... but i did say they MAY want to make it as safe as possible.
Hypothetical situation, EICR performed, Outcome satisfactory with a bunch of C3's... No work is done to improve, as none is deemed "necessary"... Accident happens, landlord is questioned as to why it happened... "Well, the EICR said it was almost safe"
Bingo Answer. It can be non compliant to the current regs on a test cert. They obviously couldn't be installed today, but the commercial element means RCD protection will almost certainly be required. Its not dangerous, its just old.well, one one hand, an EICR performed by a reputable company may say they are fine for continued use, but on the other, if these are rented out units, it may be in the best interests of safety that they do get replaced.
A general maintenance manager cannot say one way or another without testing it properly