ringer
-
I recall seeing in a DB the other day a 4mm aluminium CPC with 6mm copper line conductors (singles). In the OSG section on 'Earthing conductor and main protective bonding conductor cross-sectional areas' there is a footnote to the table (p28 red OSG, p40 green OSG) saying...
'Protective conductors (including earthing and bonding conductors) of 10mm csa or less should be copper'
This, to me, implies that ALL protective conductors <10mm should be copper.
Is this correct, and therefore the 4mm cpc mentioned above does not comply?
The circuit involved (radial for one double socket just below the DB) did very much strike me as being cobbled together with whatever the 'installer' had to hand at the time.
'Protective conductors (including earthing and bonding conductors) of 10mm csa or less should be copper'
This, to me, implies that ALL protective conductors <10mm should be copper.
Is this correct, and therefore the 4mm cpc mentioned above does not comply?
The circuit involved (radial for one double socket just below the DB) did very much strike me as being cobbled together with whatever the 'installer' had to hand at the time.