Guys I would like some opinions on the use of numeric cable core identification for LV circuits. See 514.5.

Eg. If using a 5 core YY flex with all cores coloured black and marked in white with 1 - 4 plus a green/yellow cpc. Can these be connected into a DB without any addition sleeving ie. Core 1 to L1, core 2 to L2, core 3 to L3 and core 4 to neutral.
 
i would say needs sleeving,, but what do i kno, hope this helps...;) reason being everyone else would kno after you
 
but in saying that if it is numbered 123 and 4 going to neutral,,, he need to be blind so maybe you can puncture holes for brail,,, upto you ladd!!!!!!
 
Let's talk strictly regs, sleeving or not? Cables to be connected into a DB along with cables with coloured identification.
 
For me colored sleeving is needed unless indents include the phase or neutral designation. We sleeve all cores if LV and don't sleeve instrumentation. All cores identified with silver foxes.
 
According to regs, identification is by colour or lable. I prefer colour, with additional info labelled with silver foxes ect.
 
Strictly according to the regs, then no, not required (see 514.3.1 (i) which explicitly says and/OR). The use of or implies that using either colour or one of the number/labelling schemes is the only requirement. Not sure it's good practice though.
 
I generally just make it clearly L1/L2... etc without sleeving (apart from the earth), I find this clearly shows which core is being used for which purpose.
 