S
Sparky83
Hi,
I need to install a supply for a new coffee machine. It is 6.9KW = 30Amps
It will be a 40mtr run
I think i have this right but my calculator is playing up a bit,
Ib = 6900/230 = 30A
In = 32A
In / CgxCa = Iz 32/0.88x40 = 0.9
Iz = 32+0.9 = 32.9A
Page 338 in the green Regs...
Reference Method E, Column 4
4mm Cable @ 41A
Volt Drop...
40(mtrs) x 30 x 11 / 1000 = 13.2v (which is not allowed)
6mm Cable @ 53A
40(mtrs) x 30 x 7.3 / 1000 = 8.76v (Which is allowed)
So am i right in saying that 6mm is the way to go?
the bit in red is where im must unsure
Also one further question, on page 338. column 4 it says 1 two core cable, single phase, ac or dc
But my cable will be 3 core including the earth?
The next column says 3 cor cable but than says 3 phase??
Am i right in using column number 4?
thanks
you don't say what type of cable. the table on p338 is for SWA. if you are using T/E, its table 4D5 on p340. other than that, you are right to go with 6mm
You would calculate this as 2 core, as your CPC does not normally carry any current.
As others 6mm^
Got to ask,
Would you not go one step further and work out the minimum CSA of cpc for circuit design using Adiabatic ?
I believe the Voltage Drop was the limiting factor in this case, hence the 6mm^, rather than CPC size or CCC of the cable, (4mm^ was enough for the CCC and CPC size)
So no need for the adiabatic calc.
Where have you picked the values for (Ca) & (Cg) from???
I got them from the OSG, as i didnt know the ambient temperature or if there were any cables due to not being able to see it myself yet i when for the worst case for each.
Its quite possible there s going to be other cables along parts of the route and as part of the cable run is above the false ceiling of a commerial kitchen it my be a little warmer than the norm, again hence i went for the worst case.
