hey everybody just need clarification to a question i think i got the right answer so here goes....
Q. List in the correct sequence the tests required for an installation to comply with BS 7671.
A. Continuity test
A. Insulation resistance test
A. Polarity test
A. Earth fault loop impedance
A. PSCC and PEFC if not determined by enquiry of the distributor.
A. Functional testing including, testing of RCD's and operation of all switchgear.
earth electrode/ze is missing between a and a
sorry there should of explained a bit better but i dont need an earth electrode test done as that is only required for TT systems i am working with TN systems so all is needed is a Earth Fault Loop Impedance test..
do I have to get my coat ............................phase rotation ..................sorry gather it was single phase
you just writting earth fault loop impediance, doesnt buy it for me, plus, ring final circuit conductors, and if was new install would differ from exisiting,
ring final circuit conductors comes under the same test as continuity, continiuty of conductors are to include protective conductors including main and supplementary bonding conductors, also ring final circuit conductors including protective conductors..
Visual inspection should also be before any of thoses
I wouldn't count visual inspection in the sequence of tests. They are completely seperate, hence why they call it Inspection AND Testing.
Inspection is done using the senses. Testing is done using test equipment.
nah, there seperate tests and if you look at the lists in most books there separate, all depends on what level you doing this... but your pretty dam close ;)
On site guide chapter 9 page 75
9.3.1 Testing checklist...
Please read..
im getting proximity to electrical and other services,,, you wouldnt be using he book too older regs, hahah
your right to the on site guide, but this opens up completely when your a man, and what about vold drop..
your pretty dam close tho
ok your pretty much right