Discuss List of test... in the Australia area at ElectriciansForums.net

S

Sparky12021986

hey everybody just need clarification to a question i think i got the right answer so here goes....

Q. List in the correct sequence the tests required for an installation to comply with BS 7671.

A. Continuity test
A. Insulation resistance test
A. Polarity test
A. Earth fault loop impedance
A. PSCC and PEFC if not determined by enquiry of the distributor.
A. Functional testing including, testing of RCD's and operation of all switchgear.
 
earth electrode/ze is missing between a and a

sorry there should of explained a bit better but i dont need an earth electrode test done as that is only required for TT systems i am working with TN systems so all is needed is a Earth Fault Loop Impedance test..
 
you just writting earth fault loop impediance, doesnt buy it for me, plus, ring final circuit conductors, and if was new install would differ from exisiting,
 

Reply to List of test... in the Australia area at ElectriciansForums.net

Similar Threads

I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Hi, installed some circuits in a factory. The circuits were tapped off of a busbar that goes straight to the main switchgear. From this I...
Replies
3
Views
2K
When I bought my house we had it inspected before buying to highlight faults, so the inspection and testing done by RICS Chartered Surveyor and...
Replies
13
Views
3K
https://www.linkedin.com/pulse/can-you-really-test-circuit-6-dan-jackson-fiet incasee u dont use liked in heres the article in 2 posts An...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock