R
Ryan Kavanagh
hi guys,
what is the max allowable disconnection time times under fault conditions for kitchen lighting, bedroom socket outlets and also for a shower?
thanks in advnace i appreciate all your help
ive seen in the 17th edition it says 0.4sec. is this right across the board for all the circuts.
it is 0.4 secs. for circuits up to 32A. 5 secs. for circuits over 32A and didtribution circuits.
thank you IQ. 0.2 secs,and 1 sec respectively for TT.
yes thats what i read but i thought tn systems were most common for domestic uk supply thats were i came to the 0.4sec conclusion.
TN systems are more common, but you will get plenty of TT especially in rural areas.
It very much depends on where you are, in my neck of the woods (Northumberland) I'd say it's about 50/50 TN to TT.
TT is 1 second
TN is 5 second
question is why are they different?
Electricity travels faster overhead as the ground doesn't get in the way. Therefore, the same amount of power can be transferred in 1 second with a TT system as gets transferred in 5 seconds via a TN setup.
Hope this clears it up for everyone. :innocent:
:13: genius :clap:
the 5 second rule for TN systems is set at such a level to allow discrimination between protective devices. To have distribution circuits any lower would mean that the tolerances for discrimination would need to be very tight indeed. The earthing on a TN system is said to be reliable and constant, where as a TT system is not. Also prolonged faults in a TT sytem can cause the ground potential to rise, giving a shock risk (the dead horse a few months ago)
Ryan Kavanagh,
Guest123,