The difference is the insulation is made of different materials. XLPE has a 90 degree operating temp as opposed to PVC which is 70
 
ccc? do you mean csa if so it depends who/where it was made , i,ve seen 70mm 4c with the same od. as 95mm 4c
 
if you mean CCC as current carrying capacity, then yes, XLPE does have a slighly higher current rating than PVC.
 
Tip of the day. To test if sheath is xlpe or PVC drop a piece in water. Xlpe floats and PVC sinks.

I think you mean the ''Insulation'' not the sheath. As the sheath is PVC on both XLPE and PVC insulated SWA cables mechelec...
 
what are some typical examples of when you would use XPLE over PVC please

would it be in areas with a greater ambient temp for instance???
 
Last edited by a moderator:

OFFICIAL SPONSORS

Back
Top