i am in the middle of a condition report on a large commercial building some areas are let to stores/cafes etc and we are testing these on behalf of the landlord of the main building
on one of the distribution boards was a sticker saying last tested 12/2011 so i spoke to the manager of the coffee shop and he provided me with a copy of the cirts carried out by a facilitys management company direct to the coffee shop as they didnt know the landlord was having them done.
so..........
extent of electrical installation covered by this report "whole of the buissness where practical and possible"
agreed limitations "ze and pfc found by enquiry no tests carried out to high level lighting, signs,hvac,or any final circuit needed for running the cafe during normal hours, full range of tests not carried out due to limited downtime permited, r1 & r2 calculated
so out of 40 circuits only 5 have a full set of results
1 man 1day
comments please
mark
on one of the distribution boards was a sticker saying last tested 12/2011 so i spoke to the manager of the coffee shop and he provided me with a copy of the cirts carried out by a facilitys management company direct to the coffee shop as they didnt know the landlord was having them done.
so..........
extent of electrical installation covered by this report "whole of the buissness where practical and possible"
agreed limitations "ze and pfc found by enquiry no tests carried out to high level lighting, signs,hvac,or any final circuit needed for running the cafe during normal hours, full range of tests not carried out due to limited downtime permited, r1 & r2 calculated
so out of 40 circuits only 5 have a full set of results
1 man 1day
comments please
mark