i am in the middle of a condition report on a large commercial building some areas are let to stores/cafes etc and we are testing these on behalf of the landlord of the main building

on one of the distribution boards was a sticker saying last tested 12/2011 so i spoke to the manager of the coffee shop and he provided me with a copy of the cirts carried out by a facilitys management company direct to the coffee shop as they didnt know the landlord was having them done.

so..........

extent of electrical installation covered by this report "whole of the buissness where practical and possible"

agreed limitations "ze and pfc found by enquiry no tests carried out to high level lighting, signs,hvac,or any final circuit needed for running the cafe during normal hours, full range of tests not carried out due to limited downtime permited, r1 & r2 calculated

so out of 40 circuits only 5 have a full set of results

1 man 1day

comments please
mark
 
I was asked to test a local resturant bar for insurance purposes, due to the size of the installation I suggested it would be better to do it over a couple of nights. I didn't hear from him again!! maybe I should have applied these limitations and done it in a couple of hours.
 
I was trying to find a funy remark for this but decided i could'nt. It is wrong.

saying that;-

Maybe it was signed by Micky Mouse and he is still trying to cover his ---.

Mind you, sometimes it is so f***ing hard to turn power off to test any thing.
 
At least whoever 'I&Ted' the place has been honest by stating all those limitations.
I can think of some companies that would produce a much higher percentage of 'test' results, all the IR results being '>500'.

That's the trouble with commercial premises which are live, you're so limited at what you can do.
 
The one that sticks with me .local cinema 7 screens 200 plus final circuits,central battery system etc etc.2 men one day ......also pat tested the appliances.test results consisted of 1 bit of a4 with 4 circuits marked 0.00 meg and not even hint of a clue to what they were!welcome to inspection and testing large national contractor style.
 
just noticed even the zs at the db is down as n/a and the n-e insulation lim even on the circs tested and i know the cables are all numbered
 
Suprised they didn,t issue a ticket with no test results as they came out during half day closing,or have I just given them an idea? lol
 
so hypertheticly someone gets hurt or worse on one of the untested circuits and hse get involved has everyone done their duty or do you think the client would get wrong for allowing so many limitations and not having it done out of hours
btw we are doing it again for the landlord out of hours
 
Last edited by a moderator:
I work for one of the companys doing these sort of tests YOU try telling a coffee shop/resteraunt manager that their tills will be down for 5 mins you find yourself out in the street hence ANY Limitaion placed on me by the buisness is put down as is the reason
Clients wont pay for FULL 100% tests and 3 people at night ect ect ect I test to the clients request / restrictions and CMA with limitations listed IF they dont want a full test they dont get a full test
Personaly Im not happy and would much prefer doing 100% test and do the "circuits affecting trade before they open IF Possible or asmany as I can
same doing hotel "Im neding to turn the lift off to test the electrics" "NO CHANCE"

A couple of the BIG Supermarkets I KNOW do absolutly NO Testing bar the Petrol filling stations and even then they try to get away with not closing them even done during the night
 
Last edited by a moderator:
I had a maintenance job at a hotel in Newcastle where they had a socket face damaged in a room directly behind reception. I told them to turn off the PCs so I could change it and they refused stating that they could not do this as they were vital for the running of the business. They then said I should work live as other "electricians" had done in the past. I filled in a danger notice and told them under no circumstances should the room be let as there were exposed live terminals. I also told them I'd be sending a copy of it to environmental health, the fire brigade, HSE, and the licencing authority.
Within about a minute the PCs were switched off until I'd changed the socket face and tested the circuit. Testing took ages hehe
 
I work for one of the companys doing these sort of tests YOU try telling a coffee shop/resteraunt manager that their tills will be down for 5 mins you find yourself out in the street hence ANY Limitaion placed on me by the buisness is put down as is the reason
Clients wont pay for FULL 100% tests and 3 people at night ect ect ect I test to the clients request / restrictions and CMA with limitations listed IF they dont want a full test they dont get a full test
Personaly Im not happy and would much prefer doing 100% test and do the "circuits affecting trade before they open IF Possible or asmany as I can
same doing hotel "Im neding to turn the lift off to test the electrics" "NO CHANCE"

A couple of the BIG Supermarkets I KNOW do absolutly NO Testing bar the Petrol filling stations and even then they try to get away with not closing them even done during the night

i understand what it is like i just wonder if this type of testing leaves the client open to any come backs for either not paying for out of hours or the time to shut down
 
Client would probably try the old"well they told me that was acceptable"routine, as some people do when they want the least inconvenience, a classic example is the client who wants a socket in a bathroom and when told he cant have it says "well if anything happens i,ll say I did it myself" to which I always reply "oh yes so when HSE want to jail someone you,ll take the rap? I think not!
 
I would imagine commercial organisations are like landlords in the fact that all they want to see is the box marked satisfactory regardless of the state of the installation.fine n dandy til something goes wrong then the cack will flow downhill all the way to who tested it.i do get fed up of finding faults on circuits that have supposedly been tested tho
 