IMO, it's similar to spurring a single outlet from a 2.5mm rfc. as long as it's only 1. othewrwise a FCU would be required.
But you can spur off a socket on a ring final circuit in 2.5mm to one point and that is acceptable. Although doing what the OP has stated isn't
Haven't got the BGB to hand but I didn't think it was allowed to take a spur from a radial power circuit :leaving:
As already explained, your not spurring on a radial circuit, your either extending, if taking the supply from the end of the radial, or branching if taking the supply from anywhere else along it's run...
3 X 4mm = 12mm ...most UK accessory cable terminations are now only suitable upto 10mm. Even then, the terminal screw is at it's most extended position, and often clear of any screw shields... Getting a 2.5mm into a terminal that already has 2 X 4mm is a bit of a struggle!! These cable terminals were at one time, suitable upto 12mm but was a while back....
When did this change, i cant see any difference now than 5 or 10 years ago years ago.
My question would be how is it installed,
Ccc and volt drop.
Also you can have a unprotected spur up to 3m to serve one point.
IMO I'd be questioning extending a 4mm radial that length at all lol
MK Technical:-http://www.mkelectric.com/Documents/English/EN%20MK%20Technical%20Specifications/T02%20LOGIC%20PLUS%20Tech%20355-389.pdf
sedgy34,
Strima,